Tripping GFCI during storage

I have had my trailer plugged into a GFCI for winter storage and found the outlet tripped recently. I have experimented turning off breakers and it trips if I turn the converter/fridge switch on. The surge reads E0 and 126v with everything off and I can turn the converter on when connected to a non-GFCI outlet. The fridge is off so it seems either the charging circuit is tripping the GFCI or the adapter plug is when a load is applied. I am tempted to build a custom extension cord with a 30a plug on the end but would like to find the problem first. How can I see if my charger is the problem?

I am going to charge up the trailer on the non-protected outlet then leave it in battery disconnect for now but I want to figure this out before camping season.
sailor231 is offline   Reply With Quote
Old 02-16-2019, 09:21 PM   #2
Senior Member
 
rubicon327's Avatar
 
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,123
Quote:
Originally Posted by sailor231 View Post
I have had my trailer plugged into a GFCI for winter storage and found the outlet tripped recently. I have experimented turning off breakers and it trips if I turn the converter/fridge switch on. The surge reads E0 and 126v with everything off and I can turn the converter on when connected to a non-GFCI outlet. The fridge is off so it seems either the charging circuit is tripping the GFCI or the adapter plug is when a load is applied. I am tempted to build a custom extension cord with a 30a plug on the end but would like to find the problem first. How can I see if my charger is the problem?

I am going to charge up the trailer on the non-protected outlet then leave it in battery disconnect for now but I want to figure this out before camping season.
Do you have a 2-way hot water heater? Our electric element failed hot to ground which caused the house GFI that the trailer was plugged into to trip anytime a load was applied. Keep the converter breaker off and turn on another large load like a microwave or A/C. If the GFCI trips it is likely the electric element in the HWH. It is interesting to note that while troubleshooting we learned the house GFI tripped even with the inside water heater breaker OFF and other circuits with large loads were operated. This is the GFI detecting the issue, but can lead one to believe the issue is on a circuit that it is not.
__________________
Mods to Rubicon: https://www.escapeforum.org/forums/f...tml#post249508
“One way to get the most out of life is to look upon it as an adventure.”― W.F.
rubicon327 is offline   Reply With Quote
Old 02-17-2019, 09:42 AM   #3
Senior Member
 
Vermilye's Avatar
 
Join Date: Feb 2010
Location: Oswego, New York
Trailer: 2017 Escape 21C, 2018 Ford F150
Posts: 5,363
A fault between the neutral & ground will trip a modern GFCI. If this fault is present in the heater element of the refrigerator or water heater, it will cause a trip even with the circuit breaker off. The only way to identify which device is causing the problem is to disconnect both the hot & neutral wires.

While there could also be a fault in the converter, failed heater elements are often the problem.
__________________
Jon Vermilye My Travel Blog
Travel and Photo Web Page ... My Collection of RV Blogs 2018 F150 3.5EB, 2017 21
Vermilye is offline   Reply With Quote
Old 02-17-2019, 12:21 PM   #4
Senior Member
 
rubicon327's Avatar
 
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,123
Quote:
Originally Posted by Vermilye View Post
A fault between the neutral & ground will trip a modern GFCI. If this fault is present in the heater element of the refrigerator or water heater, it will cause a trip even with the circuit breaker off. The only way to identify which device is causing the problem is to disconnect both the hot & neutral wires.

While there could also be a fault in the converter, failed heater elements are often the problem.
Jon: I think that is what I was trying to say. I’m figuring that flipping the breakers is making the OP falsely accuse the converter because it just happens to be the item with no on/off switch so it is applying load when the breaker is flipped unlike the others that require the additional step of turning the appliance on. Easy enough to check if other AC loads on other circuits also trip the GFI. I knew it was the HWH element when I disconnected it outside in the access panel and the GFI no longer tripped.

The refrigerator could be unplugged to test, but the converter needs to be disconnected within the power center so I would check the other items first.
__________________
Mods to Rubicon: https://www.escapeforum.org/forums/f...tml#post249508
“One way to get the most out of life is to look upon it as an adventure.”― W.F.
rubicon327 is offline   Reply With Quote
Old 02-17-2019, 09:59 PM   #5
Member
 
Join Date: Oct 2016
Location: Seattle, Washington
Trailer: 2018 Escape 21
Posts: 73
I have the breaker for the HW off but will pull the element when I get a chance and retry.
sailor231 is offline   Reply With Quote
Old 03-10-2019, 10:47 PM   #6
Member
 
Join Date: Oct 2016
Location: Seattle, Washington
Trailer: 2018 Escape 21
Posts: 73
I took the leads off the Hot water element and that fixed the GFCI problem. Does anyone have a part number for the element or the heater so I can order a new one?
sailor231 is offline   Reply With Quote
Old 03-11-2019, 12:49 AM   #7
Senior Member
 
rubicon327's Avatar
 
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,123
Quote:
Originally Posted by sailor231 View Post
I took the leads off the Hot water element and that fixed the GFCI problem. Does anyone have a part number for the element or the heater so I can order a new one?
suburban part # 520789
https://www.amazon.com/Suburban-5207.../dp/B003G9G4X4
__________________
Mods to Rubicon: https://www.escapeforum.org/forums/f...tml#post249508
“One way to get the most out of life is to look upon it as an adventure.”― W.F.
rubicon327 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off




» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Escape Trailer Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -5. The time now is 04:29 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2023 Social Knowledge, LLC All Rights Reserved.