Old 10-10-2016, 11:26 PM   #21
Senior Member
 
MyronL's Avatar
 
Join Date: May 2013
Location: Edgewood, New Mexico
Trailer: 2013 Esc19/'14 Silvrado
Posts: 1,666
Viaja... thanks for the great advice but think I'll just leave my battery connections the way they are. Escape set them up for me and it's all been working swell. I'm good with that.

Brian when I chose the Xantrex, probably for the extra duplex outlets and the pretty digital display, I decided to get the biggest inverter I could afford. (Go big or go home, right?) Others might need 1500 watts, but I've always been a low voltage kind of guy. Say, did I mention it's all been working swell?

I plugged in my Dewalt 3/8ths drill just yesterday.
__________________

__________________
Myron
"A billion here, a billion there...add it all up and before you know it you're talking real money." Everett Dirkson
MyronL is online now   Reply With Quote
Old 10-11-2016, 02:08 AM   #22
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 7,592
Quote:
Originally Posted by Viajante View Post
MyronL, referring back to my post #4, I think you should connect + of one battery to - of second battery with jumper cables. That should satisfy everything.
There is a cable connecting the batteries, as there must be or nothing would work. It's kinda small, but it's there.
__________________

Brian B-P is offline   Reply With Quote
Old 10-11-2016, 02:22 AM   #23
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 7,592
Quote:
Originally Posted by MyronL View Post
... think I'll just leave my battery connections the way they are. Escape set them up for me and it's all been working swell. I'm good with that.
Escape installed the inverter with the negative cable going to the frame? I haven't seen that in other Escape installations. Perhaps they only wire the 1500 watt inverters directly to the batteries.

Quote:
Originally Posted by MyronL View Post
Brian when I chose the Xantrex, probably for the extra duplex outlets and the pretty digital display, I decided to get the biggest inverter I could afford. (Go big or go home, right?) Others might need 1500 watts, but I've always been a low voltage kind of guy. Say, did I mention it's all been working swell?

I plugged in my Dewalt 3/8ths drill just yesterday.
The lowest-power corded Dewalt 3/8" drill draws 6.7 amps (at 120 volts) at full power - that's over 70 amps of 12-volt DC power, well beyond the 600 watt rating of the inverter, and more than the 60 amps of the calculations. Although the drill will work if not fully loaded, the current draw is still substantial. It will work; it's just not efficient and not tolerant of low battery voltage.
Brian B-P is offline   Reply With Quote
Old 10-11-2016, 09:57 AM   #24
Senior Member
 
MyronL's Avatar
 
Join Date: May 2013
Location: Edgewood, New Mexico
Trailer: 2013 Esc19/'14 Silvrado
Posts: 1,666
I installed the inverter. All heavier gauge than the (Escape) green wire to the frame, AWG4. Drill easily did the job. No inverter smoke, no sparks, no stress, no sweat.
__________________
Myron
"A billion here, a billion there...add it all up and before you know it you're talking real money." Everett Dirkson
MyronL is online now   Reply With Quote
Old 10-11-2016, 02:54 PM   #25
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 7,592
Quote:
Originally Posted by MyronL View Post
... think I'll just leave my battery connections the way they are. Escape set them up for me...
Quote:
Originally Posted by MyronL View Post
I installed the inverter. All heavier gauge than the (Escape) green wire to the frame, AWG4.
So Escape didn't really create this whole setup, since Myron added the inverter. I have no concerns with Escape's part, only the negative side of the inverter addition. I also have no concerns with the use of 4-gauge cables for the inverter.

By not connecting the inverter's negative cable directly to the battery, all current used by the inverter has been forced to flow through that green cable. The green cable and the cable connecting the two batteries were presumably not intended by Escape for the load of an inverter, and at least the green cable to the frame appears to be undersized for the total load with the added inverter; however, if it is large enough and the total length of cable is not too large, then everything is fine.
Brian B-P is offline   Reply With Quote
Old 10-11-2016, 04:20 PM   #26
Senior Member
 
Vermilye's Avatar
 
Join Date: Feb 2010
Location: Oswego, New York
Trailer: 2011 Escape 17B, 2016 Tacoma Off Road
Posts: 1,816
There are some advantages with going with larger than required wire. It takes voltage to push lots (well, actually, any) amps through a wire. The term is voltage drop, and it takes place all throughout the chain, including within the batteries, the wiring, and connectors, fuses, and within the inverter itself.

At low currents, the amount of voltage drop is rarely a problem, but as you get close to the rating of the wire some start to show up. Some wire is rated at 90C or higher, hot enough to concern some, particularly if you are using connectors, switches & fuse blocks that are not rated for the same or higher temperature.

To me, the real problem with voltage drop is the inverter shutting down while you still have usable battery capacity. If there is enough voltage drop that the input at the inverter is below 11 volts, most will alarm. Below 10 volts and most shut down. If your battery was really at 10 volts, that would be good since it prevents permanent damage. The reality is some of the voltage drop is in the battery, some in the wire, some in the connections, and some in the inverter. As soon as you shut the inverter off, the voltage at the inverter input jumps back to near the battery voltage, usually much higher than it was when under load.

Going with larger than required wire size will let you run the inverter longer or at times the batteries are down from full. Since most of the work is running the wiring, going with oversized wire will help prevent hassles in the long run. This is the reason Xantrex recommends at least #0 wire for its inverter installations even though their inverters under 2000 watts don't require it by code for short cable runs.
__________________
Jon Vermilye My Travel Blog
Travel and Photo Web Page ... My Collection of RV Blogs 2016 Tacoma 2011 17B
Vermilye is offline   Reply With Quote
Old 10-11-2016, 05:44 PM   #27
Senior Member
 
MyronL's Avatar
 
Join Date: May 2013
Location: Edgewood, New Mexico
Trailer: 2013 Esc19/'14 Silvrado
Posts: 1,666
Jon, Brian...Thanks, such good stuff! Will be going to Ace Hardware for some AWG2 2wire. Why take a chance?
__________________
Myron
"A billion here, a billion there...add it all up and before you know it you're talking real money." Everett Dirkson
MyronL is online now   Reply With Quote
Old 10-12-2016, 05:45 PM   #28
Senior Member
 
fudge_brownie's Avatar
 
Join Date: Nov 2008
Location: Janesville, WI, Wisconsin
Trailer: Escape 19 (sold) Escape 21 2014
Posts: 1,002
Solar and Front Storage Box for Batteries

Myron and those with solar and batteries in the front storage box.
Quote:
There are a number of reasons for not having the controller in the battery box. The first is the electrical danger. Flooded batteries may off gas, namely hydrogen, during the charge process and any chance of a spark could result in an explosion. Such events as a runaway charger or poorly programed charger can cause this as well.

Second, it is just good practice to isolate batteries from something you are adjusting or connecting in case of a dropped tool. So that slipped screwdriver does not create a light and sound show. Keeping non essential things out of the battery box and keeping the box closed while working is an important safety practice.

The third reason is the gas that is present in the battery box can cause a premature failure in the electrical components of a charger/controller, it is just plain hard on electronics. So keeping that controller outside eliminates that problem.
I recalled seeing Myron's photo of his front storage box and noticing that the solar controller/charger was mounted inside the box. When I had my 19' the front storage box had not been released, so I do not know how the batteries are stored. From the photos it appears there are two separate battery boxes, the type with vents on the lid. Is there any venting system of those battery boxes to the outside of the storage box?

If not, then some care must be taken when installing the controller/charger inside the front storage box. If the batteries are venting into the front storage box then that box becomes a battery box and the issues stated above may apply.
__________________
Paul and Janet Braun
2003 Toyota 4Runner V8 now 2012 Toyota Sequoia V8
Escape 19' 2010 now 2014 Escape 21'
fudge_brownie is offline   Reply With Quote
Old 10-12-2016, 10:36 PM   #29
Senior Member
 
MyronL's Avatar
 
Join Date: May 2013
Location: Edgewood, New Mexico
Trailer: 2013 Esc19/'14 Silvrado
Posts: 1,666
Replaced the green AWG6 wire with AWG2, to the frame and, between the battery terminals.

Expect many years service from a quality converter. Manual says the closer the solar converter is to protected batteries, the better. Have zero reason for concern about an explosion caused by a sparking solar converter. Scary thought but believe in my application irrelevant. Plenty of ventilation in my not very tightly sealed (outer) storage box. Lid always remains open when solar wires are connecting to remote panels. Not to worry.
Attached Images
File Type: jpg BaW.03.jpg (95.4 KB, 28 views)
__________________
Myron
"A billion here, a billion there...add it all up and before you know it you're talking real money." Everett Dirkson
MyronL is online now   Reply With Quote
Old 10-12-2016, 10:57 PM   #30
Senior Member
 
fudge_brownie's Avatar
 
Join Date: Nov 2008
Location: Janesville, WI, Wisconsin
Trailer: Escape 19 (sold) Escape 21 2014
Posts: 1,002
I see why the lid is always open when on solar. You are correct, no build up of the nasty gases with your install.
__________________

__________________
Paul and Janet Braun
2003 Toyota 4Runner V8 now 2012 Toyota Sequoia V8
Escape 19' 2010 now 2014 Escape 21'
fudge_brownie is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off






» Virginia Campgrounds

Reviews provided by



All times are GMT -5. The time now is 04:11 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2016, vBulletin Solutions, Inc.
Copyright 2012 Social Knowledge, LLC All Rights Reserved.