Old 02-09-2014, 10:33 AM   #21
Senior Member
 
azjack's Avatar
 
Join Date: Nov 2010
Location: Tucson, AZ, Arizona
Trailer: gone, 19 and 21
Posts: 472
ground fault plugs

On our 19 and also on the 21 the ground fault is the outside plug. All of the interiors are the same standard plug ins.
Jack
__________________

azjack is offline   Reply With Quote
Old 02-09-2014, 11:44 AM   #22
Senior Member
 
techfan's Avatar
 
Join Date: Oct 2012
Location: Longview, WA, Washington
Trailer: 2013 Escape 15B - 2014 Nissan Frontier SL
Posts: 858
Quote:
Originally Posted by azjack View Post
On our 19 and also on the 21 the ground fault is the outside plug. All of the interiors are the same standard plug ins.
Jack
The 15 has two because the run for plugs by the sink run down the driver side and behind the shower. A separate run goes along the back to reach the outside plug. The 19 and 21 must have a run that covers all the outlets which makes sense based on where the kitchen is.
__________________

__________________
Tim and Julie
2013 Escape 15B
2014 Nissan Frontier, Previous 2012 Santa Fe
techfan is offline   Reply With Quote
Old 02-09-2014, 01:06 PM   #23
Senior Member
 
Jim Bennett's Avatar
 
Join Date: Oct 2008
Location: Calgary, Alberta
Trailer: 2017 Escape 5.0 TA
Posts: 11,934
Quote:
Originally Posted by Donna D. View Post
I'm not surprised at all. The old style are inexpensive and they work just fine.
For sure they work fine, exactly the same, but for $0.60 more the upgrade is not that bad. Our electricians charge us the same either way. Just saying that more people prefer them from my experience.
Quote:
Originally Posted by azjack View Post
Maybe that plug is just 15 amps and that is the reason for the sticker on the plug that says for microwave only.
I believe that the main reason for this is that other than a few exceptions, duplex receptacles are not allowed in cabinets, and it is to discourage using it to plug in other electronics. Built in appliances that come with heavy duty cords are an exception, like garburators, microwaves, etc, are allowed to be connected in cabinets. This is the case for houses, and I believe these codes carry on into trailers.

In our last trailer, there was a black cover on the outlet prewired for a future microwave, so nothing could be plugged into it.
__________________
2017 Escape 5.0 TA
2015 Ford F150 Lariat 3.5L EcoBoost
2009 Escape 19 (previous)
“Most folks are about as happy as they make up their minds to be.” — Abraham Lincoln
Jim Bennett is offline   Reply With Quote
Old 02-11-2014, 10:53 AM   #24
Senior Member
 
MyronL's Avatar
 
Join Date: May 2013
Location: Edgewood, New Mexico
Trailer: 2013 Esc19/'14 Silvrado
Posts: 2,064
Just saying...
Attached Images
File Type: jpg usb-2.jpg (74.6 KB, 6 views)
__________________
Myron
"A billion here, a billion there...add it all up and before you know it you're talking real money." Everett Dirkson
MyronL is offline   Reply With Quote
Old 02-11-2014, 08:20 PM   #25
Senior Member
 
Join Date: Sep 2012
Location: Ottawa, Ontario
Trailer: 2013 Escape 19
Posts: 727
Myron,

They work fine if you're plugged into mains, or have an inverter, but I *always* need USB power and don't always have 120v. So I'll be building in some 12v-to-USB outlets.
__________________
Doug

2013 Escape 19 ("The Dog House") , 2012 Nissan Frontier
dbailey is offline   Reply With Quote
Old 02-12-2014, 12:37 AM   #26
Senior Member
 
Join Date: Jan 2011
Posts: 191
The rating of the circuit is with the breaker, The micro-wave has twenty amp breaker, the rest are on fifteen amp breakers, the outlet will carry the load of either one
Doug
Yukon Escape is offline   Reply With Quote
Old 02-12-2014, 12:54 AM   #27
Senior Member
 
Join Date: Jan 2014
Location: North Van., British Columbia
Trailer: 2014 Escape 19
Posts: 3,290
Quote:
Originally Posted by Yukon Escape View Post
The rating of the circuit is with the breaker,
Doug
It's been my understanding that the rating of the circuit is dependent on the guage of the wire used. A 20 amp circuit requires 12 ga. wiring. Using a 20 amp breaker doesn't make it a 20 amp circuit unless it also has the 12 ga. wires.
Ron in BC is offline   Reply With Quote
Old 02-12-2014, 01:01 AM   #28
Senior Member
 
Join Date: Jan 2011
Posts: 191
the wire is matched to the load of the breaker, both 15 and 20 can be wired with 14 gauge wire

Doug
Yukon Escape is offline   Reply With Quote
Old 02-12-2014, 09:27 AM   #29
Senior Member
 
azjack's Avatar
 
Join Date: Nov 2010
Location: Tucson, AZ, Arizona
Trailer: gone, 19 and 21
Posts: 472
electric outlet with USB

Myron, will the pictured outlet allow me to plug any of my Apple items directly into the plug. My phone, wifes I-pad and my lap top all have different sizes of transformers and we don't interchange them?
Jack
azjack is offline   Reply With Quote
Old 02-12-2014, 09:42 AM   #30
Senior Member
 
Join Date: Sep 2012
Location: Ottawa, Ontario
Trailer: 2013 Escape 19
Posts: 727
Quote:
Originally Posted by Yukon Escape View Post
the wire is matched to the load of the breaker, both 15 and 20 can be wired with 14 gauge wire
Doug, are you sure? I thought 20A required 12ga wire...
__________________

__________________
Doug

2013 Escape 19 ("The Dog House") , 2012 Nissan Frontier
dbailey is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off






» Virginia Campgrounds

Reviews provided by



All times are GMT -5. The time now is 12:32 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Copyright 2012 Social Knowledge, LLC All Rights Reserved.