What gauge electrical wire is standard in the Escapes

Just curious as to what is the standard gauge electrical wire Escape uses to feed to the 120v outlets and what gauge they use to the 12v outlets?
ADKzookeeper is offline   Reply With Quote
Old 12-21-2013, 03:40 AM   #2
Site Team
 
Donna D.'s Avatar
 
Join Date: Nov 2008
Location: Portland, Oregon
Trailer: 2014 Escape 5.0 TA
Posts: 11,040
I'm hoping it's a minimum of 12. Jim has done enough mods to his 19', and now the 21', perhaps he'll answer up and let us know.
Donna D. is offline   Reply With Quote
Old 12-21-2013, 09:23 AM   #3
Senior Member
 
Jim Bennett's Avatar
 
Join Date: Oct 2008
Location: Calgary, Alberta
Trailer: 2017 Escape 5.0 TA
Posts: 15,543
The 120V is #14, standard for the 15A circuits. Not certain on the 12V to the outlets, I would have to go to my trailer to confirm. I know the light circuits are not that big.
__________________
2017 Escape 5.0 TA
2015 Ford F150 Lariat 3.5L EcoBoost
2009 Escape 19 (previous)
“Most folks are about as happy as they make up their minds to be.” — Abraham Lincoln
Jim Bennett is offline   Reply With Quote
Old 12-21-2013, 09:31 AM   #4
Site Team
 
Donna D.'s Avatar
 
Join Date: Nov 2008
Location: Portland, Oregon
Trailer: 2014 Escape 5.0 TA
Posts: 11,040
Seems like 120v outlets for microwaves and possible places for cube heaters should be 12.... especially on the bigger trailers with longer runs. Hummm.
Donna D. is offline   Reply With Quote
Old 12-21-2013, 09:50 AM   #5
Senior Member
 
Dave Walter's Avatar
 
Join Date: Apr 2012
Location: Edmonton, Alberta
Trailer: 2013 19' & 2013 15B
Posts: 2,636
The standard 14 ga wiring should be perfectly fine for small appliances rated to about 1500 watts total per circuit.
__________________
2013 19' \ 2013 15B, 2020 Toyota 4Runner TRD Offroad

"It is better to remain silent at the risk of being thought a fool, than to talk and remove all doubt of it." - 1907, Maurice Switzer
Dave Walter is offline   Reply With Quote
Old 12-21-2013, 11:03 AM   #6
Senior Member
 
Jim Bennett's Avatar
 
Join Date: Oct 2008
Location: Calgary, Alberta
Trailer: 2017 Escape 5.0 TA
Posts: 15,543
I have installed hundreds of microwaves, and all have been on a 15A circuit. All cube heaters too are designed to be used on 15A circuits. I really know of no plug-in appliance rated higher. There certainly could be some, but almost no houses (with the exception of newer kitchens) even use 20A circuits for plugs. I know the roughed in A/C circuit on my trailer is 20A (I believe), for when one is installed.

I did run 12g (20A) circuits for 120V in my garage, but that was because of the possiblility of two tools being used at once. Most of the biggest machines in there are on 30A 240V circuits.
__________________
2017 Escape 5.0 TA
2015 Ford F150 Lariat 3.5L EcoBoost
2009 Escape 19 (previous)
“Most folks are about as happy as they make up their minds to be.” — Abraham Lincoln
Jim Bennett is offline   Reply With Quote
Old 12-21-2013, 11:55 AM   #7
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by Donna D. View Post
Seems like 120v outlets for microwaves and possible places for cube heaters should be 12.... especially on the bigger trailers with longer runs. Hummm.
As Jim suggests, household wiring provides the best basis for comparison. None of the circuits in even a 21 foot trailer will be even close to the length of a typical circuit in a house. You would have to wraps the cable around the whole perimeter of an Escape 21' at least a couple of times to reach the circuit length to the far corner of my ordinary bungalow from the panel in the opposite corner.

I noticed that heaters never exceed 1500 watts (same as the total that Dave mentioned) even though a 15 amp circuit could deliver 1800 watts; the idea is that these continuously-operating appliances must not push the circuit capacity. If you don't run anything else on the same circuit as the heater even the full 1500 watts leaves some capacity in reserve.
Brian B-P is offline   Reply With Quote
Old 12-21-2013, 12:55 PM   #8
Senior Member
 
Join Date: Sep 2009
Location: Southwick, Massachusetts
Trailer: None, sold my 2014 5.0TA
Posts: 7,124
I agree about heaters not exceeding 1500 watts, but what would be the story with blow driers? last I bought was 1875 watts.
padlin is offline   Reply With Quote
Old 12-21-2013, 02:29 PM   #9
Site Team
 
Donna D.'s Avatar
 
Join Date: Nov 2008
Location: Portland, Oregon
Trailer: 2014 Escape 5.0 TA
Posts: 11,040
I've had a 1500 W cube heater cause a plug to get hot. I'd rather that not happen if I'm running a cube heater over night. AND, I've been known to have the Mr. Coffee brewing, cube heater running on high and the microwave running while it cooks my breakfast. I can get 250 feet of 12 gauge wire for less than $100. That seems cheap compared to a fire. But, you're the experts!
Donna D. is offline   Reply With Quote
Old 12-21-2013, 02:57 PM   #10
Senior Member
 
barry's Avatar
 
Join Date: Jun 2010
Location: Fraser Valley, British Columbia
Trailer: 2012 Escape "Classic" 5.0 SA
Posts: 554
Quote:
Originally Posted by Donna D. View Post
I've had a 1500 W cube heater cause a plug to get hot. I'd rather that not happen if I'm running a cube heater over night. AND, I've been known to have the Mr. Coffee brewing, cube heater running on high and the microwave running while it cooks my breakfast. I can get 250 feet of 12 gauge wire for less than $100. That seems cheap compared to a fire. But, you're the experts!

The plug isn't getting hot because of the gauge of wire, it's getting hot because the connection of the plug to the receptacle is not conducting the electrical current that well so changing to a thicker gauge won't help.

Escape runs two circuits for 120 volt plus I also had Reace put my heater on it's own circuit as well. He ran the line for me and I installed a permanent heater in my 5.0

We've had the toaster, a hairdryer and heater all running at once and have never blown a circuit due to overload. When I traced my 120 volt lines I found that one circuit ran down one side of the trailer and the other ran down the other side.
__________________
Photography website: https://bjustice.zenfolio.com

2012 Escape "Classic" 5.0 SA / 2017 F150, 2.7 EcoBoost 4X4 Supercab
Former trailers: 2005 Escape 17B / 1972 Boler 13'
barry is offline   Reply With Quote
Old 12-21-2013, 09:04 PM   #11
Senior Member
 
Jim Bennett's Avatar
 
Join Date: Oct 2008
Location: Calgary, Alberta
Trailer: 2017 Escape 5.0 TA
Posts: 15,543
Quote:
Originally Posted by Donna D. View Post
I've had a 1500 W cube heater cause a plug to get hot. I'd rather that not happen if I'm running a cube heater over night. AND, I've been known to have the Mr. Coffee brewing, cube heater running on high and the microwave running while it cooks my breakfast. I can get 250 feet of 12 gauge wire for less than $100. That seems cheap compared to a fire. But, you're the experts!
Donna, you would have no worries in this scenario with the wiring Escape uses. For starters, the microwave is on its own circuit. Worst case scenario, is that the breaker would trip. Unless like Barry mentioned, the plug or cord is likely the weak link, and in this case it would not matter what gauge wire was used. This is the cause of 95% (just a guess, though it is by far the vast majority) of household fires, not the wiring. As a safety measure, the breaker would trip long before the wiring was in danger.

If it would set your mind at ease, you could ask Reace, but not only would the wire need to be upgraded, but the plugs and breaker too. I assume because the A/C is 20A, that the circuits could be too.

Like I mentioned above, outlets in entire households, with only a few exceptions, are all still wired at 15A, just so long as there is no more than 12 lights and/or outlets on the circuit. Our trailers are small in comparison.
__________________
2017 Escape 5.0 TA
2015 Ford F150 Lariat 3.5L EcoBoost
2009 Escape 19 (previous)
“Most folks are about as happy as they make up their minds to be.” — Abraham Lincoln
Jim Bennett is offline   Reply With Quote
Old 12-21-2013, 09:24 PM   #12
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by Donna D. View Post
I've had a 1500 W cube heater cause a plug to get hot.
As Barry explained, that's not due to inadequate wire gauge.

Quote:
Originally Posted by Donna D. View Post
I've been known to have the Mr. Coffee brewing, cube heater running on high and the microwave running while it cooks my breakfast.
Sure, but not on the same circuit - that would overload even a 12 gauge / 20 amp circuit.

Quote:
Originally Posted by Donna D. View Post
I can get 250 feet of 12 gauge wire for less than $100. That seems cheap compared to a fire.
Yes it's not a lot of money, but if every component is heavier and $100 more expensive than required, the cumulative effect is a too-heavy and unaffordable trailer. More importantly, it won't prevent a fire, anyway.

Quote:
Originally Posted by Donna D. View Post
But, you're the experts!
I claim no expertise. I only contribute my view to the discussion; it is the reader's responsibility to verify information and judge the validity of arguments.


You can use over-size wire if you decide that's best. It won't create a safety hazard, and at worst wastes money and adds a little of weight and installation hassle.
Brian B-P is offline   Reply With Quote
Old 12-22-2013, 06:44 AM   #13
Senior Member
 
cpaharley2008's Avatar
 
Join Date: Jun 2010
Location: Central, Pennsylvania
Trailer: Escape#5 2022 E19
Posts: 26,268
Donna,
If you get too many 20 amp circuits, you will need a 50 amp hookup, something to avoid at cg due to extra $$ both in overnight fees and accessories. Switch your coffee to stovetop, a lot easier solution.
__________________
Jim
Sometime life gets in the way of living.......
cpaharley2008 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off




» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Escape Trailer Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -5. The time now is 11:17 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2023 Social Knowledge, LLC All Rights Reserved.