Old 06-05-2018, 10:00 PM   #21
Senior Member
 
John in Santa Cruz's Avatar
 
Join Date: Dec 2017
Location: Santa Cruz, California
Trailer: 2014 Escape 21
Posts: 422
I don't have an inverter... but on my E21, those big red-n-black wires that exit the gooped hole, they A) aren't fused, and B) go to the power center.


IIRC, Escape offers a 1000 or 1200 watt inverter as an option? 1200 watts at 12 volts is 100 amps. you'd want 4 gauge wiring and probably a 150A fuse for that.
__________________

John in Santa Cruz is offline   Reply With Quote
Old 06-05-2018, 10:19 PM   #22
Senior Member
 
tdf-texas's Avatar
 
Join Date: Nov 2015
Location: Baytown, Texas
Trailer: 2017 21' Escape
Posts: 685
Quote:
Originally Posted by Brian B-P View Post
That's the problem - more than 30 amps used (in total for all circuits) with only 30 amp capacity. Why would the main supply from the battery to all 12 V DC circuits have only 30 amp capacity? I suppose it makes sense for only 10 gauge wire, but it seems like an unnecessary restriction, given the loads which could be connected.
I don't know the answer to that one - the WF-8955 can supply up to 55 amps so why would the current from/to the battery be limited to 30 amps? Obviously, the wire size to the battery would have to be increased to 6 gauge to handle the full amp load but the small incremental cost of the wire shouldn't be a valid reason to limit the battery current.
__________________

__________________
If It Isnít Perfect, It Isnít Finished
tdf-texas is offline   Reply With Quote
Old 06-05-2018, 10:23 PM   #23
Senior Member
 
tdf-texas's Avatar
 
Join Date: Nov 2015
Location: Baytown, Texas
Trailer: 2017 21' Escape
Posts: 685
Quote:
Originally Posted by John in Santa Cruz View Post
I don't have an inverter... but on my E21, those big red-n-black wires that exit the gooped hole, they A) aren't fused, and B) go to the power center.


IIRC, Escape offers a 1000 or 1200 watt inverter as an option? 1200 watts at 12 volts is 100 amps. you'd want 4 gauge wiring and probably a 150A fuse for that.
Without a fuse on the positive (red) wire going to the trailer, if it happened to short to ground - the wire would melt and could cause a fire. It is usually installed as close to the battery post connection as possible.

My 21 came with a GoPower GP-HS1500 1500 watt inverter.
__________________
If It Isnít Perfect, It Isnít Finished
tdf-texas is offline   Reply With Quote
Old 06-05-2018, 11:04 PM   #24
Senior Member
 
Red Dog's Avatar
 
Join Date: Oct 2015
Location: Retired from Dallas & Full-Timing, Texas
Trailer: 2017 21' Escape as of 01/16/17
Posts: 832
Tom, thanks for clarifying where these cables go. I will just be mindful and keep an eye on that 30amp fuse. I have spares.

Fred M.
__________________
Fred M.

"Whoever said retirement was overrated...
...never had an Escape"
Red Dog is offline   Reply With Quote
Old 06-06-2018, 01:15 AM   #25
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 9,848
Quote:
Originally Posted by tdf-texas View Post
I don't know the answer to that one - the WF-8955 can supply up to 55 amps so why would the current from/to the battery be limited to 30 amps?
I can only guess that the combination of 55 amp converter and only 30 amp wiring assumes that the full output of the converter is only used when there are currently active loads using at least 25 amps while the battery is charging at up to 30 amps. The assumption that charging current won't exceed 30 amps might not hold true when shore power is connected and the battery is deeply discharged, especially if there are not significant loads pulling the converter output down.

Quote:
Originally Posted by tdf-texas View Post
Obviously, the wire size to the battery would have to be increased to 6 gauge to handle the full amp load but the small incremental cost of the wire shouldn't be a valid reason to limit the battery current.
I understand and appreciate not using excess material, but in this case as long as the wire run is short (it is in a 21', and reasonable in all models since the battery and converter are logically placed relative to each other), this seems like a good idea to me.
Brian B-P is offline   Reply With Quote
Old 06-06-2018, 06:23 AM   #26
Senior Member
 
padlin's Avatar
 
Join Date: Sep 2009
Location: Southwick, Massachusetts
Trailer: 5.0 TA #6, 2012 F150 EB
Posts: 4,310
Did ETI stop installing the metal breakers they had between the + and the 12v disconnect? I believe mine has a 50A and no fuse.
__________________
Happy Motoring
Bob
padlin is offline   Reply With Quote
Old 06-06-2018, 09:34 AM   #27
Senior Member
 
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 1,889
Quote:
Originally Posted by Brian B-P View Post
That's the problem - more than 30 amps used (in total for all circuits) with only 30 amp capacity. Why would the main supply from the battery to all 12 V DC circuits have only 30 amp capacity? I suppose it makes sense for only 10 gauge wire, but it seems like an unnecessary restriction, given the loads which could be connected.
Brian: A 12V marine wiring chart I looked at (10% voltage drop - "non-critical loads") allows 10 gauge wire to be used for up to 50 amps for up to 20' length (round trip). For critical applications (3% voltage drop) you would need 4 gauge. I would consider the Escape wiring a non-critical application. Is this possibly a case where the wrong fuse is being used? If it were me I would study the wire length and consider increasing that fuse to 40 amp. Is this a feasible approach?

Quote:
Originally Posted by padlin View Post
Did ETI stop installing the metal breakers they had between the + and the 12v disconnect? I believe mine has a 50A and no fuse.
That's a good question. Can't speak for all years/models but to the best of my knowledge older trailers have a 50A thermal fuse and no blade fuses by the battery. I moved our batteries so I've seen all the wiring.
Attached Images
File Type: jpg thermal fuse.jpg (121.2 KB, 51 views)
rubicon327 is offline   Reply With Quote
Old 06-06-2018, 10:13 AM   #28
Senior Member
 
tdf-texas's Avatar
 
Join Date: Nov 2015
Location: Baytown, Texas
Trailer: 2017 21' Escape
Posts: 685
Quote:
Originally Posted by rubicon327 View Post
Brian: A 12V marine wiring chart I looked at (10% voltage drop - "non-critical loads") allows 10 gauge wire to be used for up to 50 amps for up to 20' length (round trip).
A 10% voltage drop seems to be a lot - for a 10 foot run of 10AWG wire, the voltage drop of 12 volts at the battery would be 11 volts at the fuse panel in the converter. Add in the additional voltage drops of the runs from the panel to the trailer devices and strange things start to happen.
http://www.calculator.net/voltage-dr...s=50&x=88&y=23

The fridge is a 30 amp circuit on my panel. Since it and the battery fuse are both 30 amp, we have what is known as a race condition - there is an even chance that in an over current condition, either or both fuses will blow.

It's starting to look like an area where another upgrade to the wiring is going to happen. I'm thinking 6AWG wire, a new battery cutoff switch, and a 60 amp inline fuse at the battery.

Oh, almost forgot! The 10AWG negative battery cable will need to be upgraded as well.
__________________
If It Isnít Perfect, It Isnít Finished
tdf-texas is offline   Reply With Quote
Old 06-06-2018, 03:54 PM   #29
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 9,848
Quote:
Originally Posted by rubicon327 View Post
Brian: A 12V marine wiring chart I looked at (10% voltage drop - "non-critical loads") allows 10 gauge wire to be used for up to 50 amps for up to 20' length (round trip). For critical applications (3% voltage drop) you would need 4 gauge. I would consider the Escape wiring a non-critical application. Is this possibly a case where the wrong fuse is being used? If it were me I would study the wire length and consider increasing that fuse to 40 amp. Is this a feasible approach?
It makes sense to me, and based on typical automotive practices something thinner than 6 gauge would be appropriate for 50 amps (especially high-temperature insulation), but I hesitate to suggest any smaller than traditional residential wire gauge to anyone else.
Brian B-P is offline   Reply With Quote
Old 06-06-2018, 03:57 PM   #30
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 9,848
Quote:
Originally Posted by rubicon327 View Post
Can't speak for all years/models but to the best of my knowledge older trailers have a 50A thermal fuse and no blade fuses by the battery.
Either a fuse or breaker can work, but as Tom explained it should be close to battery.
__________________

Brian B-P is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off






» Featured Campgrounds

Reviews provided by



All times are GMT -5. The time now is 08:09 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2018, vBulletin Solutions, Inc.
Copyright 2012 Social Knowledge, LLC All Rights Reserved.