Propane problem

I went on a trip ,this week,and just 1/2 hour on the road ,I pulled over for the dog pee break.The carbon monoxide detector was beeping,so I push the button and soon the light returned to normal.
I continued to my destination 4 hours further and didn't see anything to be concerned about ,I travel with the fridge running on propane and it was on and no beeping C/M detector.

Now when I went to go to bed ,I turned on the furnace and noticed it was only blowing cold air and soon the C/M detector went off again.The furnace wasn't working ,so I decided to light the burners on the stove to take the chill off,before bed.But there was very little flame coming on the burner and the second burner wouldn't even light.The fridge was still working .So I checked my propane tank even though I new it was full ,having just done that before I left,It was still full.

Then I tried turning the fridge off ,and by doing that one burner on the stove worked in full flame,but the second burner still didn't light.
Then I turned both the fridge and stove off and tried the furnace again ,with no luck just cold air.

So the fridge works alone with nothing else drawing propane and the stove works alone with one burner with nothing else drawing propane.And no furnace not at all,with everything else off.
What possibly could be wrong?
__________________
2007 Toyota Tundra
2011 Escape 15A
woodie is offline   Reply With Quote
Old 09-12-2015, 08:31 PM   #2
Senior Member
 
KarenH's Avatar
 
Join Date: Oct 2012
Location: Bellingham and Glacier, Washington
Trailer: 2013 Escape 15A
Posts: 2,051
Send a message via Skype™ to KarenH
When the new propane tanks came out several years ago, I remember being frustrated because I was using one with a flame thrower (weed burner) and couldn't get much of a flame going. It was then that I learned about opening the tanks very slowly or otherwise a check valve would be activated. Now I don't know if that stops the flow of propane or just slows it down. My experience with the flame thrower was that the flow was inhibited but not stopped. Just my anecdotal experience here.

Edited: But NEVER ignore a CO monitor beeping.
__________________
Karen Hulford
2013 Escape 15A, "Egbert"
'93 Ford 150 XLT or
'22 GMC Acadia Denali
KarenH is offline   Reply With Quote
Old 09-12-2015, 09:23 PM   #3
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by KarenH View Post
When the new propane tanks came out several years ago, I remember being frustrated because I was using one with a flame thrower (weed burner) and couldn't get much of a flame going. It was then that I learned about opening the tanks very slowly or otherwise a check valve would be activated. Now I don't know if that stops the flow of propane or just slows it down. My experience with the flame thrower was that the flow was inhibited but not stopped.
It's called an excess flow valve, it's in the hose (not the tank) but became common about the same time as the tanks got OPD valves and the new QCC style outlets, and it just limits flow rate severely. Since Woodie is getting propane, but only at very low flow rate (the refrigerator has a very small burner), this seems like a good possibility.

Another possibility is a frozen-up regulator (which can happen at well above freezing ambient temperatures due to the chilling effect of expanding propane); if that's the problem the regulator would likely be visibly covered in frost.

The last possibility I can think of is that a near-empty tank is being used (rather than the full one), and that the propane pressure is low due to chilling of the tank by evaporating propane - the tank would feel cold and the auto-changeover regulator should switch over.
Brian B-P is offline   Reply With Quote
Old 09-12-2015, 10:06 PM   #4
Senior Member
 
sunrisetrucker's Avatar
 
Join Date: Oct 2013
Location: Nanaimo Vancouver Island, British Columbia
Trailer: 2015 17b "Shelly"
Posts: 459
Could it be as simple as a pinched line allowing only a small amount of propane to flow?
sunrisetrucker is offline   Reply With Quote
Old 09-12-2015, 10:20 PM   #5
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by sunrisetrucker View Post
Could it be as simple as a pinched line allowing only a small amount of propane to flow?
That makes sense, but it is really hard to bend propane hose severely enough to kink it, and the copper tubing under the trailer is tucked out of the way and would take a severe bashing to pinch it that badly.
Brian B-P is offline   Reply With Quote
Old 09-13-2015, 04:06 PM   #6
Senior Member
 
woodie's Avatar
 
Join Date: Sep 2012
Location: Kelowna, British Columbia
Trailer: Escape 15A
Posts: 106
So far I tried to turn the propane tank valve off,then light the stove burners,until they run out of propane and go out ,then run the furnace until no propane should be in the line.Then I disconnected to tank and let it set like that for several hours,hoping that valve would re set itself.Now I shut the stove burners down and reconnected the tank and ever so slowly opened the propane tank valve .No change.

I switched the tanks and just had both tanks filled ,so they are not near empty.

Another thing is it worked for years ,and I have not changed anything to make it all of a sudden do this.
__________________
2007 Toyota Tundra
2011 Escape 15A
woodie is offline   Reply With Quote
Old 09-13-2015, 04:17 PM   #7
Senior Member
 
Jim Bennett's Avatar
 
Join Date: Oct 2008
Location: Calgary, Alberta
Trailer: 2017 Escape 5.0 TA
Posts: 15,543
A bad regulator maybe?
__________________
2017 Escape 5.0 TA
2015 Ford F150 Lariat 3.5L EcoBoost
2009 Escape 19 (previous)
“Most folks are about as happy as they make up their minds to be.” — Abraham Lincoln
Jim Bennett is offline   Reply With Quote
Old 09-13-2015, 04:45 PM   #8
Senior Member
 
C&G in FL's Avatar
 
Join Date: Jul 2014
Location: Tampa Bay Area, Florida
Trailer: 2015 Escape 5.0TA (Little Elsie) Extensively Personalized
Posts: 2,969
You mention two tanks, but are they both mounted on the trailer, or is it a simple one tank non auto change over regulator? I have never had a single feed regulator fail, though as Jim states, it could be the problem. But I would add that a few years back, shortly after the onset of OPD, l had a similar problem that resulted from a faulty pigtail, probably a malfunctioning excess flow valve. Replacing the pigtail resolved the problem. And when it is working properly, even if the excess flow valve is doing what it was designed to do, if there are no downstream leaks, it should eventually reset itself when the downstream pressure builds to a point that it is equal to the pressure on the upstream side of the excess flow valve.
__________________
What a long strange trip it’s been!
C&G in FL is offline   Reply With Quote
Old 09-13-2015, 05:00 PM   #9
Senior Member
 
Join Date: Feb 2010
Location: Alcoa, Tennessee
Trailer: 2015 5.0 TA
Posts: 419
Probably not your problem, but I discovered last year that if I tried to turn on the gas grill before I opened the tank; and then opened the tank, the flow limiter prevented the tank from providing full pressure. Turning everything off and opening the tank first solved the problem.

Dick
__________________
2015 Escape 5 TA
2016 Ford F-150
captmath is offline   Reply With Quote
Old 09-13-2015, 05:18 PM   #10
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by woodie View Post
So far I tried to turn the propane tank valve off,then light the stove burners,until they run out of propane and go out ,then run the furnace until no propane should be in the line.Then I disconnected to tank and let it set like that for several hours,hoping that valve would re set itself.
This seems like a reasonable thing to to, but if it is the excess flow valve, this will actually make the problem worse, because there will a rush of propane flow to re-fill the low-pressure plumbing.

Quote:
Originally Posted by C&G in FL View Post
And when it is working properly, even if the excess flow valve is doing what it was designed to do, if there are no downstream leaks, it should eventually reset itself when the downstream pressure builds to a point that it is equal to the pressure on the upstream side of the excess flow valve.
I agree - leaving the downstream system pressurized is the way to get the valve to reset.

Quote:
Originally Posted by captmath View Post
Probably not your problem, but I discovered last year that if I tried to turn on the gas grill before I opened the tank; and then opened the tank, the flow limiter prevented the tank from providing full pressure.
Having the grill's valve open means a big rush of propane flow when the tank valve is opened, so definitely have everything downstream turned off when opening the tank valve.
Brian B-P is offline   Reply With Quote
Old 09-13-2015, 05:21 PM   #11
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by woodie View Post
Another thing is it worked for years ,and I have not changed anything to make it all of a sudden do this.
So something broke down...

Quote:
Originally Posted by Jim Bennett View Post
A bad regulator maybe?
Bad, or not working properly due to accumulated liquid. Propane often has a bit of oil in it, which tends to accumulate in the regulator. Get enough in there, and it stops regulating properly. I've had this, and poured a millilitre or so (a "thimbleful") of oil of of the regulator after removing it. There should be no oil in a regulator.
Brian B-P is offline   Reply With Quote
Old 09-13-2015, 05:53 PM   #12
Senior Member
 
C&G in FL's Avatar
 
Join Date: Jul 2014
Location: Tampa Bay Area, Florida
Trailer: 2015 Escape 5.0TA (Little Elsie) Extensively Personalized
Posts: 2,969
Quote:
Originally Posted by Brian B-P View Post
Bad, or not working properly due to accumulated liquid. Propane often has a bit of oil in it, which tends to accumulate in the regulator. Get enough in there, and it stops regulating properly. I've had this, and poured a millilitre or so (a "thimbleful") of oil of of the regulator after removing it. There should be no oil in a regulator.
I agree, that is definitely another possibility. The fact that it was working when the trailer was last used and suddenly is not now would make me suspect that something has frozen up during a period of non use, whether inside the regulator or the excess flow mechanism. On edit, I should have mentioned that propane is actually a byproduct of the refining process, so it's anybody's guess what contaminants it could possibly contain, such as oil.
__________________
What a long strange trip it’s been!
C&G in FL is offline   Reply With Quote
Old 09-13-2015, 07:03 PM   #13
Senior Member
 
woodie's Avatar
 
Join Date: Sep 2012
Location: Kelowna, British Columbia
Trailer: Escape 15A
Posts: 106
Quote:
Originally Posted by Brian B-P View Post
This seems like a reasonable thing to to, but if it is the excess flow valve, this will actually make the problem worse, because there will a rush of propane flow to re-fill the low-pressure plumbing.


I agree - leaving the downstream system pressurized is the way to get the valve to reset.


Having the grill's valve open means a big rush of propane flow when the tank valve is opened, so definitely have everything downstream turned off when opening the tank valve.
Is the trick then to just disconnect the hose from the propane tank and leave the beyond the regulator full of propane ?.If so that is what I am doing now and will leave it for an hour or so and see if there is any change.I may just go get a new regulator in the morning.
__________________
2007 Toyota Tundra
2011 Escape 15A
woodie is offline   Reply With Quote
Old 09-13-2015, 08:50 PM   #14
Senior Member
 
woodie's Avatar
 
Join Date: Sep 2012
Location: Kelowna, British Columbia
Trailer: Escape 15A
Posts: 106
Still no change so guess I'll get a new regulator.
__________________
2007 Toyota Tundra
2011 Escape 15A
woodie is offline   Reply With Quote
Old 09-13-2015, 10:26 PM   #15
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by woodie View Post
Is the trick then to just disconnect the hose from the propane tank and leave the beyond the regulator full of propane ?
To reset the excess flow valve, I don't think you even need to disconnect the hose... just shut off the tank valve so there is zero flow, and wait a while.

There is still the trick of turning back on - I just crack the valve slightly, listen for the hissing of flowing propane, and wait until the hissing has stopped (the lines are full) before spinning it fully open. This is very different from steadily turning it open over several seconds, which is what might reasonably be understood from the instruction to "open the tank valve slowly".

Quote:
Originally Posted by woodie View Post
Still no change so guess I'll get a new regulator.
It never hurts to have a spare, even if it turn out to be something else. If the brand of regulator is not the same, the mounting screw holes might not line up... it might be worth checking which brand you have, or what the hole spacing is.

You could also get a spare "pigtail" (the hose from regulator to tank), in case the problem is a stuck or defective excess flow valve in one of the pigtails. This normally has an inverted flare on the regulator end, so it can be changed without dealing with any pipe threads (and so no thread sealant is required). To minimize excess flow valve issues, you might consider a pigtail with the higher-flow-rate excess flow valve, indicated by a green hand nut. The regular size (black hand nut; 50,000 BTU/hr) can flow more than enough for an Escape's appliances, but the the higher-rate (green; 100,000 BTU/hr) valve should be less sensitive to surges in flow.
Brian B-P is offline   Reply With Quote
Old 09-14-2015, 06:03 PM   #16
Senior Member
 
woodie's Avatar
 
Join Date: Sep 2012
Location: Kelowna, British Columbia
Trailer: Escape 15A
Posts: 106
I went and got a new regulator today and started to install it ,but the old one has the base riveted to the trailer and the screws can only be accessed if the base is removed.Escape if you are listening this makes changing regulators very difficult.I had to crawl under the trailer and turn the fittings 1/16th at a time ,being so tight the copper pipe twisted and cracked before I noticed it.So now I had to go to the store and get a new length of pipe.Crawling under again to remove the old pipe ,it runs through the frame and Escape had to of put the fittings on after threading the pipe through the frame ,because now the new pipe with fittings won't go through the same hole.Now I have to bend the pipe around and over the frame of the trailer and now my new pipe is to short.
Since I am going camping tomorrow,I macgyvered it until I have a chance to get back to the propane store,and drill out the rivets to do this properly.
But it now works ,stove furnace,fridge all at the same time.
The old regulator was full of oil.
__________________
2007 Toyota Tundra
2011 Escape 15A
woodie is offline   Reply With Quote
Old 09-14-2015, 06:24 PM   #17
Senior Member
 
Jim Bennett's Avatar
 
Join Date: Oct 2008
Location: Calgary, Alberta
Trailer: 2017 Escape 5.0 TA
Posts: 15,543
Glad to hear you got it working.

A bunch of years back, previous to owning an Escape, I had issues with propane very similar to yours. What it was, was a waxy white substance, kinda greasy, that was clogging the lines. I had to clean out my regulator, and blow out the lines, and all was well. I got rid of the bottle that caused the grief too. I must have got the contamination when the bottle was filled.
__________________
2017 Escape 5.0 TA
2015 Ford F150 Lariat 3.5L EcoBoost
2009 Escape 19 (previous)
“Most folks are about as happy as they make up their minds to be.” — Abraham Lincoln
Jim Bennett is offline   Reply With Quote
Old 09-14-2015, 08:55 PM   #18
Senior Member
 
Join Date: Oct 2013
Location: Monroe, Michigan
Trailer: escape 21may 2014
Posts: 168
When we fill propane tanks that have run completely empty we always purge them. You may have some air in the tank.
burrab2002 is offline   Reply With Quote
Old 09-14-2015, 11:53 PM   #19
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by woodie View Post
I went and got a new regulator today and started to install it ,but the old one has the base riveted to the trailer and the screws can only be accessed if the base is removed.Escape if you are listening this makes changing regulators very difficult.
That's surprising, and definitely something to check out when getting familiar with the trailer. Thanks for the tip.

Quote:
Originally Posted by woodie View Post
I had to crawl under the trailer and turn the fittings 1/16th at a time ,being so tight the copper pipe twisted and cracked before I noticed it.So now I had to go to the store and get a new length of pipe.Crawling under again to remove the old pipe ,it runs through the frame and Escape had to of put the fittings on after threading the pipe through the frame ,because now the new pipe with fittings won't go through the same hole.Now I have to bend the pipe around and over the frame of the trailer and now my new pipe is to short.
Regulators are often mounted on the threaded rod which is used to clamp down the tanks, which means it moves when the tanks are moved, which means that the regulator output is connected to the trailer with a hose. The point is that a hose is a valid alternative to copper line, especially if you need something that needs fancy routing and a store is open which sells them. A 3/8" copper line would have a 3/8" SAE female swivel on each end, and that's a common hose configuration.

Quote:
Originally Posted by woodie View Post
The old regulator was full of oil.
Well at least we know what the problem was...
The old regulator may be fine once drained. I think it's at least worth keeping around as a spare.
Brian B-P is offline   Reply With Quote
Old 09-15-2015, 12:08 AM   #20
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by C&G in FL View Post
... I should have mentioned that propane is actually a byproduct of the refining process, so it's anybody's guess what contaminants it could possibly contain, such as oil.
Trivia: propane can come out of the well with oil, but is commonly a component of the liquids (they're liquid when under pressure) which come out of natural gas wells along with the gas. The propane is separated from this mix (natural gas liquids if it came with gas), and the heavier parts (butane, etc.) are mostly used as components of various chemicals including plastics. The separation can be imperfect, plus oils can be picked up from equipment along the way.

I wouldn't say that anything is a byproduct of refining - all components are valuable products, and dealing with the balance of those components is one of the challenges of the oil and gas industry... you don't get to pick one part and just get that.
Brian B-P is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off




» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Escape Trailer Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -5. The time now is 09:26 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2023 Social Knowledge, LLC All Rights Reserved.