30 amp in a 50 amp site

Greetings from Poulsbo Wa. We put our down payment on the 19. I have a question. When camping with a 30 amp plug, what happens when the site only has 50 amps.
chris valenta is offline   Reply With Quote
Old 10-23-2014, 12:04 AM   #2
Site Team
 
rbryan4's Avatar
 
Join Date: Jun 2014
Location: Canyon Lake, Texas
Trailer: 2015 19 "Past Tents", 2021 F150 Lariat 2.7L EB
Posts: 10,222
Quote:
Originally Posted by chris valenta View Post
Greetings from Poulsbo Wa. We put our down payment on the 19. I have a question. When camping with a 30 amp plug, what happens when the site only has 50 amps.
You need a dogbone. Its a 50 amp to 30 amp adapter. Should be standard equipment for any 30 amp RV. You never know when you might need it.

Its ok to hook up a 30 amp trailer to a 50 amp site, because you can't draw more than 30 amps anyway with a 30 amp main breaker.

Amazon.com: Camco 55175 18" PowerGrip Dogbone Electrical Adapter with Handle: Automotive
__________________
"You can't buy happiness, but you can buy an RV. And that is pretty close."
rbryan4 is offline   Reply With Quote
Old 10-23-2014, 12:10 AM   #3
Senior Member
 
Join Date: Jul 2009
Location: Silverdale, Washington
Trailer: No more Escape 21
Posts: 412
Chris, welcome neighbor to the Escape family. I think Walmart in Poulsbo has the adapter and I know that Clear Creek RV in Silverdale has the adapter. If you have any questions on the 19 (I'm a former 19 owner) or just want to BS, let me know (I'm in Silverdale)
__________________
2008 Toyota Highlander
RickM is offline   Reply With Quote
Old 10-23-2014, 12:29 AM   #4
Member
 
chris valenta's Avatar
 
Join Date: Oct 2014
Location: poulsbo, Washington
Trailer: 2015 19ft
Posts: 34
Thanks for all the info, from the newest newbee.
chris valenta is offline   Reply With Quote
Old 10-23-2014, 05:33 AM   #5
Senior Member
 
C&G in FL's Avatar
 
Join Date: Jul 2014
Location: Tampa Bay Area, Florida
Trailer: 2015 Escape 5.0TA (Little Elsie) Extensively Personalized
Posts: 2,960
Chris, if you can't get the adapter at Walmart or the "local" RV outlet, they also have them at Csmping World.
__________________
What a long strange trip it’s been!
C&G in FL is offline   Reply With Quote
Old 10-23-2014, 06:22 AM   #6
Senior Member
 
cpaharley2008's Avatar
 
Join Date: Jun 2010
Location: Central, Pennsylvania
Trailer: Escape#5 2022 E19
Posts: 26,268
I have not seen an "exclusive 50 amp campground" but do see "50 amp sites available" which implies that in addition to the 30 amp hookups there are 50 amp hookups, both at the same pedestal. So you should be fine staying there with your stock power cord.
__________________
Jim
Sometime life gets in the way of living.......
cpaharley2008 is offline   Reply With Quote
Old 10-23-2014, 07:10 AM   #7
Senior Member
 
Jim Bennett's Avatar
 
Join Date: Oct 2008
Location: Calgary, Alberta
Trailer: 2017 Escape 5.0 TA
Posts: 15,532
Yeah, what Jim said. Any site with a 50A hookup I have seen, also has 30A, and 15A too.
__________________
2017 Escape 5.0 TA
2015 Ford F150 Lariat 3.5L EcoBoost
2009 Escape 19 (previous)
“Most folks are about as happy as they make up their minds to be.” — Abraham Lincoln
Jim Bennett is offline   Reply With Quote
Old 10-23-2014, 08:10 AM   #8
Senior Member
 
Join Date: Mar 2013
Location: Yellow Springs, Ohio
Trailer: 2013 Escape 19
Posts: 709
We stayed in a 50A-only park near Bardstown KY once. They happened to have a supply of adapters behind the counter to sell. To their credit, they did try to let people know when making reservations. That's probably the only place we've needed to use a 50 to 30 Amp adapter.
Parker is offline   Reply With Quote
Old 10-23-2014, 08:13 AM   #9
Member
 
Join Date: Sep 2014
Location: Central, New Jersey
Trailer: 2015 Escape 21, 2014 Four Wheel Campers Grandby
Posts: 35
I would disagree with the statement that it is ok connect a 30A Trailer to a 50A connection at the site unless you are 100% sure that all of the wiring leading up to the 30A main breaker is rated for 50A or there is a 30A breaker built into the 50A to 30A cable at the post. The 30A main breaker in the camper will not protect against a partial short in the wiring leading up to it.
NJ Joe is offline   Reply With Quote
Old 10-23-2014, 08:19 AM   #10
Senior Member
 
Join Date: Feb 2010
Location: Phoenix Metro Area, Arizona
Trailer: 2014 Escape 19
Posts: 767
Quote:
Originally Posted by NJ Joe View Post
I would disagree with the statement that it is ok connect a 30A Trailer to a 50A connection at the site unless you are 100% sure that all of the wiring leading up to the 30A main breaker is rated for 50A or there is a 30A breaker built into the 50A to 30A cable at the post. The 30A main breaker in the camper will not protect against a partial short in the wiring leading up to it.
I agree in theory, but not in practice. By the same logic you should never plug a 16g extension cord into a 15 or 20 amp outlet. And your big screen TV with a (probably) 5 amp internal fuse/breaker should never be plugged into a 15 or 20 amp circuit.
jamman is offline   Reply With Quote
Old 10-23-2014, 08:37 AM   #11
Member
 
Join Date: Sep 2014
Location: Central, New Jersey
Trailer: 2015 Escape 21, 2014 Four Wheel Campers Grandby
Posts: 35
In the case of the TV example, most (probably all) TVs sold in the US have gone through UL testing to ensure the combination of power cord size and internal fuse does not cause a fire hazard. In the case of the extension cord example, there are a lot of house fires started by faulty wiring and improper use of extension cords. I agree that the risk in this case would be small if an inspection of the wiring was done prior to making the connection, but any time you deviate from accepted standards, you should really do a risk analysis. In most cases, it is not practical to do a complete risk analysis and you are better off just following the standards.
NJ Joe is offline   Reply With Quote
Old 10-23-2014, 08:56 AM   #12
Senior Member
 
MyronL's Avatar
 
Join Date: May 2013
Location: ..., New Mexico
Trailer: 2013 Esc19/'14 Silvrado
Posts: 4,193
Do a risk analysis? We're campers! Sounds like anal government bureaucratic double-speak.
__________________
Myron
"A billion here, a billion there...add it all up and before you know it you're talking real money." Everett Dirkson
MyronL is offline   Reply With Quote
Old 10-23-2014, 09:33 AM   #13
Senior Member
 
Vermilye's Avatar
 
Join Date: Feb 2010
Location: Oswego, New York
Trailer: 2017 Escape 21C, 2018 Ford F150
Posts: 5,363
I can't think of any situation where a fault in the cord or connector (or anywhere before the 30 amp trailer breaker) would cause more than 30 amps, but less than 50 amps to flow. Most faults will be a direct short, which will cause far more than 50 amps to flow. Under a direct short, there will be little difference between the time a 30 amp or 50 amp breaker opens.

The #10 power cord will carry enough current to open a 50 amp breaker without damage.
__________________
Jon Vermilye My Travel Blog
Travel and Photo Web Page ... My Collection of RV Blogs 2018 F150 3.5EB, 2017 21
Vermilye is offline   Reply With Quote
Old 10-23-2014, 10:13 AM   #14
Site Team
 
rbryan4's Avatar
 
Join Date: Jun 2014
Location: Canyon Lake, Texas
Trailer: 2015 19 "Past Tents", 2021 F150 Lariat 2.7L EB
Posts: 10,222
What Jon said.
__________________
"You can't buy happiness, but you can buy an RV. And that is pretty close."
rbryan4 is offline   Reply With Quote
Old 10-23-2014, 10:13 AM   #15
Senior Member
 
Join Date: Mar 2013
Location: Yellow Springs, Ohio
Trailer: 2013 Escape 19
Posts: 709
Quote:
Originally Posted by Vermilye View Post
The #10 power cord will carry enough current to open a 50 amp breaker without damage.
Interesting thought. I made up a #14 power cord for plugging in to a 20 amp outlet when I don't need to run the air conditioner, rather than drag out the 30 amp cable. So if I run my light duty power cord, made with #14 wire, to a 20 amp plug into a couple of adapters to connect to a 50 amp service, my power cord may be the fuse in the circuit. I don't know why I would want to do that, but I can picture a pretty spectacular result!
Parker is offline   Reply With Quote
Old 10-23-2014, 10:41 AM   #16
Member
 
Join Date: Sep 2014
Location: Central, New Jersey
Trailer: 2015 Escape 21, 2014 Four Wheel Campers Grandby
Posts: 35
I completely respect everyone's opinion here. I have read through many posts from Jon and others on the forum, and have learned quite a bit. I have one additional question to throw out there. If the 50A breaker can provide adequate protection for a 30A trailer, why do campgrounds have a separate 30A breaker instead of just tying the 30A receptacle to the 50A breaker to reduce costs.
NJ Joe is offline   Reply With Quote
Old 10-23-2014, 11:06 AM   #17
Senior Member
 
cpaharley2008's Avatar
 
Join Date: Jun 2010
Location: Central, Pennsylvania
Trailer: Escape#5 2022 E19
Posts: 26,268
If you have the Progressive Industries EMS protection installed by ETI you will not need to worry about the "What if" happenings.
__________________
Jim
Sometime life gets in the way of living.......
cpaharley2008 is offline   Reply With Quote
Old 10-23-2014, 11:33 AM   #18
Senior Member
 
Jim Bennett's Avatar
 
Join Date: Oct 2008
Location: Calgary, Alberta
Trailer: 2017 Escape 5.0 TA
Posts: 15,532
Quote:
Originally Posted by NJ Joe View Post
If the 50A breaker can provide adequate protection for a 30A trailer, why do campgrounds have a separate 30A breaker instead of just tying the 30A receptacle to the 50A breaker to reduce costs.
So your trailer can be connected, as the cord end won't fit into a 50A receptacle.

In the case of a fault, there is no doubt that #10 wire would trip a 50A breaker. The only potential issue is if you somehow overloaded the circuit with appliances drawing too much current. This could potentially cause the #10 cable to act as a fuse if it were protected at 50A. However, the 30A breaker in the trailer would protect you in this case, tripping if the draw became excessive. This would leave the cable to the pedestal as the only improperly protected section in the circuit, and the only thing that could happen to it is a fault from being cut, in which case the breaker would still trip as Jon explained.

Bottom line. There really is no need to be concerned.
__________________
2017 Escape 5.0 TA
2015 Ford F150 Lariat 3.5L EcoBoost
2009 Escape 19 (previous)
“Most folks are about as happy as they make up their minds to be.” — Abraham Lincoln
Jim Bennett is offline   Reply With Quote
Old 10-23-2014, 12:25 PM   #19
Senior Member
 
Vermilye's Avatar
 
Join Date: Feb 2010
Location: Oswego, New York
Trailer: 2017 Escape 21C, 2018 Ford F150
Posts: 5,363
I made one of these as a way to use a light cord when plugging into a 15/20 amp receptacle. It also gives me a practical way to carry a spare Marinco twist lock connector since that can be difficult to replace on the road.
Attached Thumbnails
ASG_6494.jpg  
__________________
Jon Vermilye My Travel Blog
Travel and Photo Web Page ... My Collection of RV Blogs 2018 F150 3.5EB, 2017 21
Vermilye is offline   Reply With Quote
Old 10-23-2014, 12:49 PM   #20
Senior Member
 
thoer's Avatar
 
Join Date: Oct 2009
Location: Galesville, Wisconsin
Trailer: 2017 21 "Blue II" & 2017 Highlander XLE (previously 2010 17B "Blue" & 2008 Tacoma)
Posts: 4,232
Quote:
Originally Posted by Vermilye View Post
I made one of these as a way to use a light cord when plugging into a 15/20 amp receptacle. It also gives me a practical way to carry a spare Marinco twist lock connector since that can be difficult to replace on the road.
Smart thinking Jon.
__________________
Eric (and Mary who is in no way responsible for anything stupid I post)

"Beware of false knowledge; it is more dangerous than ignorance." George Bernard Shaw
thoer is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off




» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Escape Trailer Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -5. The time now is 12:44 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2023 Social Knowledge, LLC All Rights Reserved.