Battery fusing question

I am putting Battleborn Lithium GC2 format batteries in my new 5.0. They will be individually fused & switched prior to being combined and fused again for going to distribution. I will be wiring each battery thru the fuse & switch to the combining block using equal length runs to balance the load & charging (I'm starting with 2 batteries but allowing for 3 in my setup.)

My question concerns the size of the fuse at the individual batteries. The specs on the battery indicates that the BMS will allow 100 amp continuous with up to 200 amps for 30 seconds (and more for 5 seconds but that isn't useful to me). My biggest individual draw will be a 2000 watt inverter (166+ amps) plus whatever else.

With the batteries load balanced, what should I fuse each battery at? I currently have 100 amp fuses which should work, but was thinking it wouldn't hurt to get some larger ones. The fuses mount right at the battery post so changing a blown one is the same effort as temporarily totally removing it and connecting direct to the battery while waiting to get another fuse.

FYI - the attached pic shows the battery fuse setup I'll use: one at each battery and one for the output of the combining block. The largest of this type of fuse is 300 amps so that is what I have for the combined output. At the distribution board I have a 400 amp T fuse at its input (I got that fuse before deciding on the balanced battery setup).
Attached Thumbnails
Screenshot_2019-08-25-09-51-46.jpg  
__________________
Tom W
( 5.0TA, "Gray Ghost" )
StillCampin is offline   Reply With Quote
Old 08-25-2019, 12:36 PM   #2
Senior Member
 
Iowa Dave's Avatar
 
Join Date: Aug 2015
Location: Benton County, Iowa
Trailer: 2013 Escape 21 Classic Number 6, pulled by 2018 Toyota Highlander
Posts: 8,234
Your wire size comes into play here too. Make sure it’s heavy enough to handle the loads you’re talking about. I’m no expert here but I’ve seen melted insulation before the fuse opened a few times. And real tight connections.
Iowa Dave
__________________
Ain’t no trouble jacking a double Burma Shave
Dave
Iowa Dave is offline   Reply With Quote
Old 08-25-2019, 06:04 PM   #3
Senior Member
 
StillCampin's Avatar
 
Join Date: Jul 2018
Location: Cottonwood, Arizona
Trailer: 2019 5.0TA pulled by Ram 3500 diesel dually
Posts: 286
Quote:
Originally Posted by Iowa Dave View Post
Your wire size comes into play here too. Make sure it’s heavy enough to handle the loads you’re talking about. I’m no expert here but I’ve seen melted insulation before the fuse opened a few times. And real tight connections.
Iowa Dave
I have a (limited) supply of various sizes of cable including 4/0 for the main from combiner bar to distribution, 2/0, 1/0, 2, 4, etc for other purposes. I have a hydraulic crimper for the 2/0 & smaller cable lugs that does 4/0 with effort but it really squishes the lug so my “pound with a hammer” crimping tool will likely get some use.

My little refillable butane torch isn’t useful for soldering the big lugs so I’ll get a torch fitting for the skinny propane bottles (Bernzomatic).

I have a torque screwdriver for the inch-pound electrical fittings. It only goes down to 10 so the lightest might get tight but it goes to 50 so it will do most. I used my battery powered foot-pound socket wrench-style torque indicator to get the 60 ft lb for the Anderson.
__________________
Tom W
( 5.0TA, "Gray Ghost" )
StillCampin is offline   Reply With Quote
Old 08-25-2019, 06:10 PM   #4
Senior Member
 
Iowa Dave's Avatar
 
Join Date: Aug 2015
Location: Benton County, Iowa
Trailer: 2013 Escape 21 Classic Number 6, pulled by 2018 Toyota Highlander
Posts: 8,234
Sounds like you are ready to do some electrical work. Good luck, I hope it comes out like you planned.
Iowa Dave
__________________
Ain’t no trouble jacking a double Burma Shave
Dave
Iowa Dave is offline   Reply With Quote
Old 08-26-2019, 12:40 AM   #5
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
I would fuse for the lowest-capacity component (conductor, connector, etc) that the fuse is protecting... not just enough for the load device. Of course is your wiring is appropriate, the corresponding fuse will be more than enough for the load.

So, for instance, if your wiring is good for 300 amps, that's what I would use, even if the inverter might be okay with 167 amps.
Brian B-P is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off




» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Escape Trailer Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -5. The time now is 06:27 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2023 Social Knowledge, LLC All Rights Reserved.