Quote:
Originally Posted by HABBERDABBER
Thank you for your response. I get it. I think my extension cords are 10' or 15', a fraction of the 50' you used. And I'm running a PWM, probably.
So what's the voltage drop for a 15', 12g cord? I'm too lazy to look it up, I guess.
And what I have has worked to charge the house batteries.
Voltage......Smoltage!
|
I can only find charts for solid wire, and extension cords are generally stranded, so the numbers below are an under-estimate. For a given gauge, voltage drop will be slightly higher for stranded than solid, since stranded has air gaps where solid does not.
20A via 15 feet of 12 gauge copper would be 1.19V.
20A via 15 feet of 12 gauge aluminum would be 1.95V.
See
Voltage Drop Calculator
Here is the specific wire I am using for a 25 foot cable to handle 60A 12V with capability to scale up if needed. Low voltage drop. Low heat dissipation. This is a pair of 25 foot 6 gauge stranded copper cables:
https://www.amazon.com/dp/B00LIB8AQG...roduct_details
Another option is jumper cables. They are lower quality than welding cable, but are still rated for much high current than extension cables. It's possible a cheap pair of jumper cables would have much lower voltage drop than a 120V extensions cord.