02-10-2020, 01:40 PM
|
#21
|
Senior Member
Join Date: Jun 2010
Location: Central, Pennsylvania
Trailer: Escape#5 2022 E19
Posts: 26,268
|
You cobble together a grounding plug. Here are some threads
https://www.escapeforum.org/forums/f...r-13161-2.html
__________________
Jim
Sometime life gets in the way of living.......
|
|
|
02-10-2020, 04:22 PM
|
#22
|
Junior Member
Join Date: Aug 2017
Location: Seattle, Washington
Trailer: 21, 2018
Posts: 11
|
?
When I go to your link I see this:
Sorry - no matches. Please try some different terms
|
|
|
02-10-2020, 09:27 PM
|
#23
|
Senior Member
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,146
|
Quote:
Originally Posted by Twgose
And what do you do with the grounding issue when using a generator? Go into by-pass mode?
|
Buy or make a bonding plug and plug it into one of the unused outlets on the generator.
https://www.microair.net/products/ge...12272654155860
|
|
|
02-11-2020, 08:00 AM
|
#24
|
Senior Member
Join Date: Jun 2010
Location: Central, Pennsylvania
Trailer: Escape#5 2022 E19
Posts: 26,268
|
Quote:
Originally Posted by Twgose
When I go to your link I see this:
Sorry - no matches. Please try some different terms
|
Sorry, I fixed the link now... https://www.escapeforum.org/forums/f...r-13161-2.html
__________________
Jim
Sometime life gets in the way of living.......
|
|
|
02-12-2020, 11:08 AM
|
#25
|
Junior Member
Join Date: Aug 2017
Location: Seattle, Washington
Trailer: 21, 2018
Posts: 11
|
Thank You
Thank You
|
|
|
02-12-2020, 08:11 PM
|
#26
|
Senior Member
Join Date: Dec 2019
Location: Boulder, Colorado
Trailer: 2020 Escape 5.0TA "Zen"
Posts: 1,390
|
How many people are having trouble or getting errors from their surge protector? Is this a rare occurrence or are other people having this issue?
What are the error codes people are seeing?
|
|
|
02-12-2020, 08:30 PM
|
#27
|
Senior Member
Join Date: Feb 2010
Location: Oswego, New York
Trailer: 2017 Escape 21C, 2018 Ford F150
Posts: 5,370
|
So far the only error codes I have seen since 2011 are low voltage & reversed polarity. Both are fairly rare, but I have seen them more than once & further checking indicated that the EMS was producing correct information.
|
|
|
02-12-2020, 10:20 PM
|
#28
|
Senior Member
Join Date: Feb 2015
Location: Lanesboro, MN, between Whalan and Fountain, Minnesota
Trailer: 2016 Bigfoot 25RQ - (2018 Escape 5.0 sold)
Posts: 2,174
|
Quote:
Originally Posted by UncleTim
How many people are having trouble or getting errors from their surge protector? Is this a rare occurrence or are other people having this issue?
What are the error codes people are seeing?
|
This is our third EMS and none have given us any problems.
We didn't need one until we came back to the campground and our converter was toast. Talked to others there and the one's who had protectors had no problems but the rest of us had various ruined appliances. Our weekend was ruined. We were lucky it didn't happen on a long camping trip
Just like insurance, you really hope you never need to use the EMS.
Enjoy,
Perry
__________________
Those who know everything use pens. Intelligent people use pencils.
|
|
|
02-13-2020, 05:56 AM
|
#29
|
Senior Member
Join Date: Jun 2010
Location: Central, Pennsylvania
Trailer: Escape#5 2022 E19
Posts: 26,268
|
Quote:
Originally Posted by UncleTim
How many people are having trouble or getting errors from their surge protector? Is this a rare occurrence or are other people having this issue?
What are the error codes people are seeing?
|
You will get a card with the error codes and meanings which I put near the display.
This is from their website:
E 0 - Normal Operating Condition
E 1 - Reverse Polarity (hot and neutral wires reversed)
E 2 - Open Ground (no ground wire connection)
E 3 - Line 1 High Voltage (line voltage above 132V)
E 4 - Line 1 Low Voltage (line voltage below 104V)
E 5*- Line 2 Voltage High (Line voltage above 132V)
E 6*- Line 2 Voltage Low (Line voltage below 104V)
E 7 - Line Frequency High (line frequency above 69Hz)
E 8 - Line Frequency Low (line frequency below 51Hz)
E 9 - Data Link Down (call technical support)
E 10 - Replace Surge Protector Module (call Progressive
Industries Tech Support)
*note 5&6 applicable only to 50 amp set up
__________________
Jim
Sometime life gets in the way of living.......
|
|
|
02-13-2020, 08:02 AM
|
#30
|
Senior Member
Join Date: Mar 2013
Location: North of Danbury, Wisconsin
Trailer: 2018 Escape 21C
Posts: 3,033
|
The faults we have gotten are E3 (high voltage ) and E4 (low voltage )
My Fluke meter showed neither condition was present at the time the EMS showed fault
Is there a way to widen the voltage perimeters or increase the time delay for the unit to respond ?
.
|
|
|
02-13-2020, 11:25 AM
|
#31
|
Senior Member
Join Date: Oct 2013
Location: Phoenix, Arizona
Trailer: 2015 Escape 19 "Seventy Degrees"
Posts: 3,495
|
Only had one low voltage at COE park. Guys came right over and replaced breaker, and it was fine the rest of the stay.
|
|
|
02-17-2020, 02:57 PM
|
#32
|
Senior Member
Join Date: Sep 2016
Location: Redwood City, California
Trailer: 2017 Escape 19
Posts: 286
|
I've never had any issues with mine. It's tripped multiple times, but for legitimate reasons. Once for swapped neutral/hot at someone's house, and several times for low voltage. The low voltage in particular seems to happen more during heat waves. In one case it actually tripped and registered 70V on input after a windstorm. Low enough to potentially damage the AC, I'd imagine, and possibly even the converter.
|
|
|
02-17-2020, 07:38 PM
|
#33
|
Senior Member
Join Date: May 2015
Location: Bellingham, Washington
Trailer: 5.0 TA "Sea'scape"
Posts: 278
|
For newer folks like me, it seems this discussion is about the Progressive Industries EMS-HW30C electrical Management System (EMS) <www.progressiveindustries.net>. I believe this is the model that ETI installs as an option (currently $400 CDN). Yes?
I note that this EMS has two built-in time delays, 15 seconds or 136 seconds, that activate if AC power in interrupted or the EMS detects a fault condition. The longer delay is for use with air conditioners that don't have a built-in time delay.
Does anyone know whether the currently-installed air conditioner installed by ETI has a built-in time delay? And whether the EMSs installed by ETI are set for 15 or 136 seconds?
Progressive Industries also manufactures a portable EMS with similar features, the EMS-PT30X. No installation hassles but easy to forget or have walk away.
Currently, the EMS-HW30C sells for $218 USD at bestconverter.com and $258 USD on Amazon.
|
|
|
02-17-2020, 10:49 PM
|
#34
|
Senior Member
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,146
|
Quote:
Originally Posted by HawkeyeEZ
I note that this EMS has two built-in time delays, 15 seconds or 136 seconds, that activate if AC power in interrupted or the EMS detects a fault condition. The longer delay is for use with air conditioners that don't have a built-in time delay.
Does anyone know whether the currently-installed air conditioner installed by ETI has a built-in time delay? And whether the EMSs installed by ETI are set for 15 or 136 seconds?
|
ETI has traditionally installed the HW30C EMS with the jumper pulled within the unit which means it has the 136 second delay. This was required as the Dometic air conditioners don’t have an internal time delay for compressor protection. Fast forward to the use of the digital thermostats (both the white 1st generation and newer black capacitive touch versions). These thermostats have a 2 minute compressor time delay feature built in. One can confirm in their manual. I suspect ETI still pulls the jumper but actually doesn’t have to now. Best to check with them. I have a custom mini-split A/C which has its own compressor protection and I also installed my own EMS and left the jumper installed. It is nice to have power to the trailer after only 15 seconds.
|
|
|
02-17-2020, 11:42 PM
|
#35
|
Senior Member
Join Date: Sep 2013
Location: Ventura County, California
Trailer: 2013 19 Escape
Posts: 7,204
|
Quote:
Originally Posted by rubicon327
ETI has traditionally installed the HW30C EMS with the jumper pulled within the unit which means it has the 136 second delay. This was required as the Dometic air conditioners don’t have an internal time delay for compressor protection. Fast forward to the use of the digital thermostats (both the white 1st generation and newer black capacitive touch versions). These thermostats have a 2 minute compressor time delay feature built in. One can confirm in their manual. I suspect ETI still pulls the jumper but actually doesn’t have to now. Best to check with them. I have a custom mini-split A/C which has its own compressor protection and I also installed my own EMS and left the jumper installed. It is nice to have power to the trailer after only 15 seconds.
|
So Dave that is the reason it takes so long for compressor to start ? Pat
|
|
|
02-18-2020, 11:51 AM
|
#36
|
Senior Member
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,146
|
Quote:
Originally Posted by Patandlinda
So Dave that is the reason it takes so long for compressor to start ? Pat
|
Yes, so when you initially plug in or have a reason for the EMS to shut down you are going to wait 2 minutes, 16 secs. for the EMS to reset and allow power to the trailer and then wait another 2 minutes for the thermostat to allow the compressor to start. You can shave off two minutes if the jumper is installed in the EMS. For those that don't have the jumper because ETI removed it you would need to call Progressive Industries to see if they would send you one.
Customer Service
Phone: 1-800-307-6702 press 1
progressive@powerprodllc.com
|
|
|
02-18-2020, 12:04 PM
|
#37
|
Senior Member
Join Date: Sep 2013
Location: Ventura County, California
Trailer: 2013 19 Escape
Posts: 7,204
|
Quote:
Originally Posted by rubicon327
Yes, so when you initially plug in or have a reason for the EMS to shut down you are going to wait 2 minutes, 16 secs. for the EMS to reset and allow power to the trailer and then wait another 2 minutes for the thermostat to allow the compressor to start. You can shave off two minutes if the jumper is installed in the EMS. For those that don't have the jumper because ETI removed it you would need to call Progressive Industries to see if they would send you one.