Adding a second 50amp ATS

I have solar with a Magnum inverter and want to add a second ATS so as to have three inputs shore, Onan gen, solar does the inverter go into the gen on the new ATS?
Routemaster is offline   Reply With Quote
Old 03-01-2023, 02:32 AM   #2
Site Team
 
John in Santa Cruz's Avatar
 
Join Date: Dec 2017
Location: Mid Left Coast, California
Trailer: 2014 Escape 21
Posts: 5,122
Normally, you plug your shore cord into the generator. If you want an ATS there, it would do the same thing, connect the generator output to the shore power input

Wait, your talking about a big 5th wheel? This forum is for the molded fiberglass trailers made by Escape. We have 30A service, and no room for onboard generators....
John in Santa Cruz is offline   Reply With Quote
Old 03-01-2023, 12:32 PM   #3
Senior Member
 
Join Date: Oct 2019
Location: Western, Wisconsin
Trailer: WTB: E19
Posts: 238
Quote:
Originally Posted by John in Santa Cruz View Post
Normally, you plug your shore cord into the generator. If you want an ATS there, it would do the same thing, connect the generator output to the shore power input

Wait, your talking about a big 5th wheel? This forum is for the molded fiberglass trailers made by Escape. We have 30A service, and no room for onboard generators....
John... Say it isn't so... A 2017 Heartland Arlington isn't a fiberglass
__________________
Bill & Cindy Evans
"Remember, we are guests in nature....no one likes a houseguest who trashes the place"
Escape_19 is offline   Reply With Quote
Old 03-01-2023, 12:43 PM   #4
Site Team
 
Donna D.'s Avatar
 
Join Date: Nov 2008
Location: Portland, Oregon
Trailer: 2014 Escape 5.0 TA
Posts: 11,023
Quote:
Originally Posted by Escape_19 View Post
Jon... Say it isn't so... A 2017 Heartland Arlington isn't a fiberglass
I'm not looking it up, but while it may be fiberglass (panels), it's not molded fiberglass.
__________________
Donna D.
Ten Forward
2014 Escape 5.0TA
Donna D. is offline   Reply With Quote
Old 03-01-2023, 02:07 PM   #5
Senior Member
 
Centex's Avatar
 
Join Date: Feb 2020
Location: East of Austin, Texas
Trailer: 2021 Escape 5.0 / 2022 F150 SuperCab
Posts: 2,866
If using two 2-source ATS in series to accommodate 3 'hard wired' power sources
  • Assuming the ATS are both labelled for "Shore In" and "Gen In' with shore taking priority when it's available
  • Assuming you want the 3-source priority to be shore, then gen, then inverter (battery / solar)
  • Connect shore and gen to ATS#1 as normal
  • Connect ATS#1 Output to ATS#2 Shore In
  • Connect Inverter output to ATS#2 Gen In
  • Connect ATS#2 Output to house AC distribution system
IF your system auto-starts the Gen in the absence of shore power, and you want to go to Inverter in absence of shore power (as at a "no generators" campsite), you'll have to manually stop the Gen start-up to force the use of the inverter source.

There are 3-source transfer switches available, too.
__________________
Alan E.
2021 Escape 5.0 / 2022 F150 Lariat SuperCab 6.5' box / Centex's 2021 5.0 Modifications
Centex is offline   Reply With Quote
Old 03-01-2023, 08:01 PM   #6
Site Team
 
John in Santa Cruz's Avatar
 
Join Date: Dec 2017
Location: Mid Left Coast, California
Trailer: 2014 Escape 21
Posts: 5,122
Quote:
Originally Posted by Centex View Post
If using two 2-source ATS in series to accommodate 3 'hard wired' power sources
  • Assuming the ATS are both labelled for "Shore In" and "Gen In' with shore taking priority when it's available
  • Assuming you want the 3-source priority to be shore, then gen, then inverter (battery / solar)
  • Connect shore and gen to ATS#1 as normal
  • Connect ATS#1 Output to ATS#2 Shore In
  • Connect Inverter output to ATS#2 Gen In
  • Connect ATS#2 Output to house AC distribution system
IF your system auto-starts the Gen in the absence of shore power, and you want to go to Inverter in absence of shore power (as at a "no generators" campsite), you'll have to manually stop the Gen start-up to force the use of the inverter source.

There are 3-source transfer switches available, too.
usually the inverter is behind the main breaker panel, as it only runs some loads and not others, for instance, you don't want dual rooftop AC units on an inverter, nor do you want your DC power converter (battery charger) to run off the inverter.... The inverter output goes to a transfer switch which is fed from the main panel, and outputs to a subpanel for the circuits that it does drive, such as microwave, and 120V outlets.
John in Santa Cruz is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off




» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Escape Trailer Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -5. The time now is 04:44 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2023 Social Knowledge, LLC All Rights Reserved.