Quote:
Originally Posted by sameo416
Does the circuit tester indicate if you have a live ground? Some do and some don’t.
If you have hot and neutral reversed a multimeter should still show voltage slot to slot. Narrow slot to ground should show 120 V, so that's not proof of a reversal.
The EMS is a system that can take power on and off. What you're describing sounds like you may have an intermittent neutral or hot connection. I would step through the system from power connector to internal outlets to check voltage at each point NH NG HG. Output of the convertor important too.
|
If you're still having problems I would ditch the outlet tester and use a multimeter to check voltage at each step between the outlet in the house you're using to an outlet in the trailer. Anywhere you can access the connection until you isolate the issue. Don’t assume the house outlet is good, test at each connection.
What you should see is this when plugged into the house outlet:
HN (short slot to long slot) 110/120 V hot-neutral
HG (short slot to pin) 110/120 V hot-ground
NG (long slot to pin) 0 V neutral-ground
If HN is not 110/120, you have a hot or neutral broken
If HG is not 110/120 you have a hot or ground broken
If NG is not 0, you likely have a H-N reversed
If HG is 110/120 but HN is 0, broken neutral
If HN is 110/120 but HG is 0, broken ground
You likely don’t have a HN short or a HG short as either should trip the house breaker quickly.
If its intermittent I would start by swapping out the extension cord. If not the extension it could be a 2 person job, one to watch the meter and the other to shake wires to look for an intermittent connection.
This is a reasonable resource:
What Does a Hot Ground Reverse Receptacle Test Reading Mean?
https://www.doityourself.com/stry/wh...e-reading-mean