Old 10-01-2017, 06:03 PM   #1
Senior Member
 
Join Date: Sep 2012
Location: Ottawa, Ontario
Trailer: 2013 Escape 19
Posts: 743
Electrical gremlins and plumbing stacks...

A month or so ago we were on the road with our 19 when a pretty significant rain storm came through. A lot of rain pounding down hard, and we were driving through it. For the next couple of days we had a variety of different electrical problems -- inconsistent furnace function, battery drawing down way too quickly for the load we had on it, outside light working erratically, etc... Obvious conclusion was that we had water inside. Sure enough, once everything had time to dry out, everything worked properly again.

So the hunt for the water infiltration point began... I was suspicious of a few things, but particularly the plumbing vent stack. What I learned investigating this did not make me happy.

It looks like these things are installed in a couple of pieces. Cut a hole in the foot plate for the stack pipe, seal this piece down and caulk the pipe around it. Add the riser part of the vent and seal/caulk it down. The cap on top is then snaps in place.

The problem I found is that the caulk between the vent pipe and that first foot plate was not doing its job. It was a putty of some sort, and it had somehow worked its way up so that it was 1/2" above the foot plate. If I poured water down the outside of the vent pipe, it just disappeared somewhere inside the trailer. I cut a hole in the plywood wall beside the dinette and I could see the water running down the vent pipe.

The *real* problem is that there is no way to fix this caulk joint! There's no way to get a finger, or a tool, or the end of a caulk gun down between the vent riser and the stack pipe. Looks like the only option is to completely remove the vent cover and start over again.

These plumbing vents are a real bad design...

I guess you typically won't get water under the vent cap, since you'd have to have water flowing up hill, but it's not like we ever pull these things at highway speeds through the rain, is it?

I looked at the vent over the sink on the passenger side and while it wasn't nearly as bad, any water poured in beside the vent pipe did slowly leak into the trailer. At least there's no significant electrical hiding downstream from this vent.

At this point it looks like the only real solution is to completely tear off and replace both vents...

Has anybody else seen problems with water infiltration around the plumbing vents?

Thanks for any insight...
__________________
Doug

2013 Escape 19 ("The Dog House") , 2018 Ford F150
dbailey is offline   Reply With Quote
Old 10-01-2017, 06:41 PM   #2
Senior Member
 
Join Date: Aug 2012
Location: N/A, Indiana
Trailer: Escape
Posts: 976
Pictures ?
__________________
"Never argue with an idiot. They only bring you down to their level and beat you with experience." George Carlin
Jubal is offline   Reply With Quote
Old 10-01-2017, 06:50 PM   #3
Senior Member
 
Patandlinda's Avatar
 
Join Date: Sep 2013
Location: Ventura County, California
Trailer: 2013 19 Escape
Posts: 7,203
Quote:
Originally Posted by Jubal View Post
Pictures ?
Also would be very interested in some pictures . Thankyou . Pat
Patandlinda is offline   Reply With Quote
Old 10-01-2017, 07:00 PM   #4
Senior Member
 
PGDriver's Avatar
 
Join Date: Nov 2008
Location: Southern Alberta, Alberta
Trailer: 2015 Escape 5.0TA
Posts: 1,734
Admitted the vent cap system is poorly engineered and as I believe there is no expansion joint in the vent stack it would be not be advisable to attach the stack to the roof rigidly, the joint or caulking must be flexible to allow for expansion and also flex of the roof. Most RV manufacturers use them and unfortunately they are industry standard.
What I have done in the past is with the cap removed swab the inside lightly with acetone then pump enough liquid butyl to seal the cap to the stack to the roof. This has always worked long term for me.


Cheers
Doug
__________________
Cheers
Doug
PGDriver is offline   Reply With Quote
Old 10-01-2017, 07:43 PM   #5
Senior Member
 
Join Date: Sep 2009
Location: Southwick, Massachusetts
Trailer: None, sold my 2014 5.0TA
Posts: 7,124
How about using the Cyclone if it fits, you can drive as fast as you want and not get rain in it.

__________________
Happy Motoring
Bob
padlin is offline   Reply With Quote
Old 10-01-2017, 08:15 PM   #6
Senior Member
 
Join Date: Mar 2016
Location: West Coast, Florida
Trailer: None now
Posts: 1,266
padlin, I wonder what a tree branch would do to it? It looks like it would rip the pipe out if one hooked into that wind vane part.
wetzk is offline   Reply With Quote
Old 10-01-2017, 08:28 PM   #7
Senior Member
 
cpaharley2008's Avatar
 
Join Date: Jun 2010
Location: Central, Pennsylvania
Trailer: Escape#5 2022 E19
Posts: 26,268
I would insert a smaller diameter piece of hose, maybe 1.5" black drain hose down inside to where the joint is and secure it under the cap and replace the cap. Any water should go down the inner hose past the joint.
__________________
Jim
Sometime life gets in the way of living.......
cpaharley2008 is offline   Reply With Quote
Old 10-01-2017, 08:57 PM   #8
Senior Member
 
Join Date: Sep 2012
Location: Ottawa, Ontario
Trailer: 2013 Escape 19
Posts: 743
I'm not sure I can get a picture that shows the problem, but I will do what I can tomorrow evening.

Doug, I think liquid butyl might do the trick -- I didn't know such a thing existed.

One of the problems with the existing stack is that there is some play in the ABS vent pipe. As it moves, it messes up the caulk. I suspect that's how the original caulk got ruined. But if I completely filled the well with liquid butyl, that should hold the ABS from moving. I just hope that the liquid butyl sticks to the vent well enough that the movement of the ABS doesn't break the seal.

(I also suspect that this problem exists in most Escape trailers, but that it hasn't been noticed because it's rare that enough water gets in to cause problems.)

The existing well is rather dirty, so getting it clean enough for anything to stick will be a challenge...
__________________
Doug

2013 Escape 19 ("The Dog House") , 2018 Ford F150
dbailey is offline   Reply With Quote
Old 10-01-2017, 08:57 PM   #9
Senior Member
 
Join Date: Sep 2009
Location: Southwick, Massachusetts
Trailer: None, sold my 2014 5.0TA
Posts: 7,124
Quote:
Originally Posted by wetzk View Post
padlin, I wonder what a tree branch would do to it? It looks like it would rip the pipe out if one hooked into that wind vane part.
I think the idea is to not hit trees.
__________________
Happy Motoring
Bob
padlin is offline   Reply With Quote
Old 10-01-2017, 09:18 PM   #10
Senior Member
 
Join Date: Sep 2012
Location: Ottawa, Ontario
Trailer: 2013 Escape 19
Posts: 743
Quote:
Originally Posted by cpaharley2008 View Post
I would insert a smaller diameter piece of hose, maybe 1.5" black drain hose down inside to where the joint is and secure it under the cap and replace the cap. Any water should go down the inner hose past the joint.
Jim, I'm not sure what you're suggesting. I'll try some ascii art to explain the situation...

Code:
                 |-----------------------|  cap
                 |                       |
                 |  |     |     |     |  |
                    |     |     |     | 
                    |    X|     |X    | <- vent wall
  roof  ------------|---- |     | ----|--------------  
                          |     |
                          |     |
                          |     |ABS


The 'X' marks the location of the caulk that has failed. Without that caulk, water can run down the outside of the ABS pipe into the trailer instead of down the inside into the tank...


__________________
Doug

2013 Escape 19 ("The Dog House") , 2018 Ford F150
dbailey is offline   Reply With Quote
Old 10-02-2017, 01:08 AM   #11
Senior Member
 
Patandlinda's Avatar
 
Join Date: Sep 2013
Location: Ventura County, California
Trailer: 2013 19 Escape
Posts: 7,203
Quote:
Originally Posted by dbailey View Post
Jim, I'm not sure what you're suggesting. I'll try some ascii art to explain the situation...

Code:
                 |-----------------------|  cap
                 |                       |
                 |  |     |     |     |  |
                    |     |     |     | 
                    |    X|     |X    | <- vent wall
  roof  ------------|---- |     | ----|--------------  
                          |     |
                          |     |
                          |     |ABS


The 'X' marks the location of the caulk that has failed. Without that caulk, water can run down the outside of the ABS pipe into the trailer instead of down the inside into the tank...


I wonder when we are washing the roof of the trailer ,using a sprayer , is water getting in the trailer ? Pat
Patandlinda is offline   Reply With Quote
Old 10-02-2017, 07:57 AM   #12
Senior Member
 
cpaharley2008's Avatar
 
Join Date: Jun 2010
Location: Central, Pennsylvania
Trailer: Escape#5 2022 E19
Posts: 26,268
I understand now, I thought the joint was within the pipe going down inside, so my suggestion is now void. Sorry about that. But seems to me if you remove the cap, a good flexible sealant should allow movement without an opening and since it is not visible, just fill the entire space between the pipe and vent wall to insure coverage.
__________________
Jim
Sometime life gets in the way of living.......
cpaharley2008 is offline   Reply With Quote
Old 10-02-2017, 01:36 PM   #13
Senior Member
 
AKCamper's Avatar
 
Join Date: Jul 2015
Location: Juneau, Alaska
Trailer: 2016 Escape 19
Posts: 555
Quote:
Originally Posted by cpaharley2008 View Post
I understand now, I thought the joint was within the pipe going down inside, so my suggestion is now void. Sorry about that. But seems to me if you remove the cap, a good flexible sealant should allow movement without an opening and since it is not visible, just fill the entire space between the pipe and vent wall to insure coverage.
I wonder if it would be a good idea to drill a small hole into the vent pipe to allow water that accumulates to drain down after applying the flood coat of sealant as you suggest?
AKCamper is offline   Reply With Quote
Old 10-02-2017, 01:39 PM   #14
Senior Member
 
cpaharley2008's Avatar
 
Join Date: Jun 2010
Location: Central, Pennsylvania
Trailer: Escape#5 2022 E19
Posts: 26,268
That may work, like me drilling a small hole in the bottom of my marker lights to dissipate condensation. Or you can wait and see if evaporation takes care of any water intrusion.
__________________
Jim
Sometime life gets in the way of living.......
cpaharley2008 is offline   Reply With Quote
Old 10-02-2017, 07:14 PM   #15
Senior Member
 
Join Date: Sep 2009
Location: Southwick, Massachusetts
Trailer: None, sold my 2014 5.0TA
Posts: 7,124
Could you make an extension for the tube of caulk, something like a piece of rubber tubing?
__________________
Happy Motoring
Bob
padlin is offline   Reply With Quote
Old 10-02-2017, 07:36 PM   #16
Senior Member
 
Join Date: Sep 2012
Location: Ottawa, Ontario
Trailer: 2013 Escape 19
Posts: 743
Quote:
Originally Posted by cpaharley2008 View Post
I understand now, I thought the joint was within the pipe going down inside, so my suggestion is now void. Sorry about that. But seems to me if you remove the cap, a good flexible sealant should allow movement without an opening and since it is not visible, just fill the entire space between the pipe and vent wall to insure coverage.
That's my current thought. There isn't room to get a finger in there to form a putty, but something that I can manipulate with a small stick or chopstick would do the job. That's why I was interested in the notion of "liquid butyl" that Doug mentioned. I haven't looked around to see if I can find it locally, but now that I understand the problem I'm not in such a hurry.
__________________
Doug

2013 Escape 19 ("The Dog House") , 2018 Ford F150
dbailey is offline   Reply With Quote
Old 10-02-2017, 07:39 PM   #17
Senior Member
 
Join Date: Sep 2012
Location: Ottawa, Ontario
Trailer: 2013 Escape 19
Posts: 743
Quote:
Originally Posted by Patandlinda View Post
I wonder when we are washing the roof of the trailer ,using a sprayer , is water getting in the trailer ? Pat
I suspect so...

If you want to test, pull the cap off (rotate it 1/8 turn to release) and use a jug to pour a little water between the vent wall and the ABS pipe. If the water doesn't pool there, it must be leaking into the trailer.

I didn't get home in time to get photos before dark tonight, and I'm out tomorrow evening, but I'll try to do that some time this week.
__________________
Doug

2013 Escape 19 ("The Dog House") , 2018 Ford F150
dbailey is offline   Reply With Quote
Old 10-02-2017, 09:40 PM   #18
Senior Member
 
Patandlinda's Avatar
 
Join Date: Sep 2013
Location: Ventura County, California
Trailer: 2013 19 Escape
Posts: 7,203
Quote:
Originally Posted by dbailey View Post
I suspect so...

If you want to test, pull the cap off (rotate it 1/8 turn to release) and use a jug to pour a little water between the vent wall and the ABS pipe. If the water doesn't pool there, it must be leaking into the trailer.

I didn't get home in time to get photos before dark tonight, and I'm out tomorrow evening, but I'll try to do that some time this week.
Doug still interested in your photo's . Confused exactly where . Don't understand why it couldn't be caulked . Will need to take a look but I see I think it is diclor around Vent. Sorry for my confusion . Pat
Patandlinda is offline   Reply With Quote
Old 10-02-2017, 10:02 PM   #19
Senior Member
 
Join Date: Sep 2012
Location: Ottawa, Ontario
Trailer: 2013 Escape 19
Posts: 743
Quote:
Originally Posted by Patandlinda View Post
Doug still interested in your photo's . Confused exactly where . Don't understand why it couldn't be caulked . Will need to take a look but I see I think it is diclor around Vent. Sorry for my confusion . Pat
The reason I can't use normal the caulking is simply that there isn't enough room. The place that needs caulk is 3 or 4 inches down in the gap between the ABS pipe and the side of the vent. And that gap is not wide enough to see what you're doing or to work the angle of the caulk gun correctly. Putty doesn't work because I can't get my finger in the gap to shape the putty.

Something thin enough to self-level and fill the whole space sounds like the right solution. If I can't find something liquid, I will try a large volume of normal caulk and use a stick or something similar to spread it around.
__________________
Doug

2013 Escape 19 ("The Dog House") , 2018 Ford F150
dbailey is offline   Reply With Quote
Old 10-02-2017, 10:07 PM   #20
Senior Member
 
gbaglo's Avatar
 
Join Date: Oct 2008
Location: North Vancouver, British Columbia
Trailer: 2009 Escape 17B 2020 Toyota Highlander XLE
Posts: 17,136
I don't get it. If this vent is so common in the RV industry, there must be an easier solution.
__________________
What happens to the hole when the cheese is gone?
- Bertolt Brecht
gbaglo is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off




» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Escape Trailer Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -5. The time now is 03:48 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2023 Social Knowledge, LLC All Rights Reserved.