Quote:
Originally Posted by rubicon327
Steve: The Honda EU2000i and 2200i have a floating neutral and also a ground terminal. Are you saying to use the neutral bonding plug in an unused receptacle on the generator AND a ground rod connected to the ground terminal for true protection?
|
If you want to provide a full grounding system to earth, yes. All tying the neutral to ground does is allow the EMS to detect it is not floating.
Earthing of an electrical system provides for a low resistance path for fault currents to flow, both to protect people who might touch the energized metal frame of a device and to help ensure overcurrent protection operates quickly, (circuit breaker),
Without the earth ground it is possible a fault in an appliance could lead to the energizing of the skin of the appliance and someone touching it could complete the circuit and receive a shock. Traditional circuit breakers do not operate quickly enough to provide shock protection, which is why an earthed grounding system is required by code in distribution systems.
A circuit protected by a GFCI is not dependent on a ground connection, and still provides shock protection even using a generator with no earth connection.
How that risk of shock applies to a fibreglass trailer on rubber tires is a more complicated question.