Originally Posted by Centex
So Gus, according to the referenced codes would a GFPD be required at all three 'levels' in the array with 3 or more PV Panels depicted in the the crude single-line diagram attached?
|
(1) Do the PV DC circuits exceed 30V or 8 amperes? Your labeling indicates yes.
(2) Does your PV bus combiner have overcurrent protection? See NEC §690.9. l'd recommend using a fused combiner box. I have also seen several RVers use the MC4 inline fuse holders.
Then turn to §690.41(B)(2): "The faulted circuits shall be controlled by one of the following methods:
(1) The current-carrying conductors of the faulted circuit shall be automatically disconnected.
(2)The device providing ground fault protection fed by the faulted circuit shall automatically cease to supply power to output circuits and interrupt the faulted PV system dc circuits from the ground reference in a functionally grounded system."
Without knowing all the details in your "crude single-line diagram", L2 seems the correct location. You need to determine the correct positioning given all your system details.
Victron, Midnite Solar, Morningstar, and others have excellent application notes on using PV GFPD. Recommend consulting them with your details.
73/gus