Quote:
Originally Posted by rubicon327
Nice work getting it going again! The electrode is a 2 prong design to also sense flame. My guess is similar to yours. The old electrode was fine but you had a bad thermocouple so it failed to tell the board you had flame.
|
Thanks! It’s a relief.
As I understand from a previous post, the electrode itself is the thermocouple. Unlike the pilot in the oven, or like the one in our gas fireplace, there isn’t a separate item that functions as a thermocouple. Current between the rods of the electrode passes through the flame better than it does through air, and the module needs to see a certain return. Little or no return in air, sufficient return in flame (ionized was the term).
I love learning how this stuff works so I can figure it out in the future.
|
|
|
07-29-2022, 07:39 PM
|
#22
|
Senior Member
Join Date: Jan 2014
Location: Lancaster, Virginia
Trailer: 2022 Escape 21C
Posts: 118
|
Excellent timing for me on your post Brett. I just turned on the water heater in preparation for tonight’s dishes and the ignition started acting up. The heater would light, fault light cuts off, flame goes out, fault light on heater reignites but by the third try the heater stayed lit. I had the same trouble this morning but I had to reset the switch after 3 attempts to light. The heater worked fine yesterday. I now have a good troubleshooting guide. Thank you
Ed
Escape Reality
|
|
|
10-30-2022, 04:37 PM
|
#23
|
Member
Join Date: Nov 2016
Location: Nanaimo, British Columbia
Trailer: 2017 Escape 19
Posts: 64
|
It was only a temporary tease.
On my next outing in the first week of October the water heater only worked for a few days then it went back to the same fail state as before.
I ordered up the ignitor board from Dinosaur electronics, and today I’m in the trailer to install it.
I read that it is different but didn’t absorb what the difference was. Now I see that it is a larger board in every direction and the ignitor wire connects differently form the factory part.
The original connection is a spade connector.
The Dinosaur connects similar to a spark plug boot.
Gonna have to find a different connector or a different ignitor wire.
Also, the original cover won’t fit. Will search this forum to see if there is a ready-made solution.
|
|
|
10-30-2022, 05:12 PM
|
#24
|
Member
Join Date: Nov 2016
Location: Nanaimo, British Columbia
Trailer: 2017 Escape 19
Posts: 64
|
Quote:
Originally Posted by Brookfielder
On my next outing in the first week of October the water heater only worked for a few days then it went back to the same fail state as before.
I ordered up the ignitor board from Dinosaur electronics, and today I’m in the trailer to install it.
I read that it is different but didn’t absorb what the difference was. Now I see that it is a larger board in every direction and the ignitor wire connects differently form the factory part.
The original connection is a spade connector.
The Dinosaur connects similar to a spark plug boot.
Gonna have to find a different connector or a different ignitor wire.
Also, the original cover won’t fit. Will search this forum to see if there is a ready-made solution.
|
I see that I am to blame for my problem.
I ordered on Amazon. I needed part number UIB S.
Somehow I chose UIB S POST. The photo in the listing I chose was of the UIB S, but the part number was not what I needed.
Hoping they accept a return, ordering the correct part.
Sometimes when giving my opinion to someone, and I’m trying to instill confidence I’ll say, “I’ve been wrong twice before, but I’m pretty sure about this.”
Now I’m going to have to say I’ve been wrong three times. Dang.
|
|
|
12-11-2022, 04:59 PM
|
#25
|
Member
Join Date: Nov 2016
Location: Nanaimo, British Columbia
Trailer: 2017 Escape 19
Posts: 64
|
Water heater not working
I wonder if anyone who has already done this can offer guidance regarding the connection to the new board?
The terminology between manufacturers doesn’t match. I saw warnings that connectors amy need to be re-pinned, and it appears to be true.
Power and NC seem to be common between the two.
V1 could be Valve?
Test, Sense, and Ground are good questions.
|
|
|
12-11-2022, 05:00 PM
|
#26
|
Member
Join Date: Nov 2016
Location: Nanaimo, British Columbia
Trailer: 2017 Escape 19
Posts: 64
|
Water heater not working
Back sides
|
|
|
12-11-2022, 07:59 PM
|
#27
|
Senior Member
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,146
|
Quote:
Originally Posted by Brookfielder
I wonder if anyone who has already done this can offer guidance regarding the connection to the new board?
The terminology between manufacturers doesn’t match. I saw warnings that connectors amy need to be re-pinned, and it appears to be true.
Power and NC seem to be common between the two.
V1 could be Valve?
Test, Sense, and Ground are good questions.
Attachment 66185
|
I haven’t replaced one myself but have researched these boards. It should be plug and play with the Dinosaur UIB-S and Suburban water heater
The only thing you should need to do is clip a resistor on the board for instant fire. Instructions should have been included.
|
|
|
12-11-2022, 09:23 PM
|
#28
|
Member
Join Date: Nov 2016
Location: Nanaimo, British Columbia
Trailer: 2017 Escape 19
Posts: 64
|
Quote:
Originally Posted by rubicon327
I haven’t replaced one myself but have researched these boards. It should be plug and play with the Dinosaur UIB-S and Suburban water heater
The only thing you should need to do is clip a resistor on the board for instant fire. Instructions should have been included.
|
Thank you for your insight. I agree with you.
I was wondering about the instant fire option. I couldn't say whether this water heater is instant fire or not.
|
|
|
12-11-2022, 09:25 PM
|
#29
|
Senior Member
Join Date: Mar 2016
Location: New Mexico, New Mexico
Trailer: 2017 E19
Posts: 613
|
Dave,
I have fortunately not had to replace my furnace nor my hot water heater boards (yet). Why would I want to have, and what is "instant fire"?
thanks
|
|
|
12-11-2022, 10:56 PM
|
#30
|
Senior Member
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,146
|
Quote:
Originally Posted by MVA
Dave,
I have fortunately not had to replace my furnace nor my hot water heater boards (yet). Why would I want to have, and what is "instant fire"?
thanks
|
I’m no expert but it appears that you want instant-fire for water heaters and refrigerators. Found online: “These delayed 3-try ignitor boards with 20 Second purge cycles and LOCAL flame sense also incorporate an option jumper. Removal of the jumper, for water heater and refrigerator use only, converts the board to instant fire with one Minute purge cycle between the three ignition tries.”
http://www.dinosaurelectronics.com/I...UIB_S_inst.pdf
|
|
|
12-12-2022, 09:57 AM
|
#31
|
Senior Member
Join Date: Mar 2016
Location: New Mexico, New Mexico
Trailer: 2017 E19
Posts: 613
|
Thanks Dave for finding this application sheet.
|
|
|
|
|