We picked up our new E19 on 3/23 and camped in Blaine, Wa. Well since it was cold the first thing we noticed was that the furnace would not put out warm air from the blower and the only way to get the blower to stop running was to disconnect the power and turn off the battery. Turning off at the thermostat had no effect, the blower just kept blowing air.
We are home in Houston now and I took off the cover outside and after cleaning the sail switch and reinstalling had the same problem. The trouble shooting light on the mother board is flashing two red flashes meaning a "flame sense fault". I have tried to get any air out of the the propane lines by running all the appliances and still no problem resolution.
My model no is DFSAD12131 and I just sent an email to Dometic with the same info.
Just wondering if anyone else has run into this problem and what solution finally solved the problem. I did not find anything in past threads about this type of problem. Thanks in advance for any help.
|
You definitely want Dometic to repair this under warranty as the board is not cheap.
After repair, there may be something you might want to think about. The DFSAD12131 (along with a number of your RV devices) doesn't like voltages over 13.5 vdc. The converter in your trailer puts out 13.6 vdc in absorption and 14.4 vdc while in bulk mode. If you have solar, it gets even worse.
https://www.escapeforum.org/forums/f...tml#post278437
I now have voltage regulators on all my devices.