Old 06-01-2018, 11:14 PM   #61
Senior Member
 
tdf-texas's Avatar
 
Join Date: Nov 2015
Location: Baytown, Texas
Trailer: 2017 21' Escape - upgraded version
Posts: 2,697
Quote:
Originally Posted by Ron in BC View Post
It was a lot of years ago when I wrote the exam, and only as part of my training, not to become an electrician, but back then the Canadian Electrical Code required a dedicated circuit for microwaves. Rule26-704(9) That was based on the general rule that all appliances, like fridges required their own circuits.
Ron
Did some Google research on Canadian code and found this:
26-720 [d] Each receptacle installed in a cupboard, wall cabinet or enclosure for the use of a microwave oven in accordance with rule 26-710 [i] shall be supplied by a branch circuit that does not supply any other outlets and this circuit shall not be considered as forming part of the circuits required under rule 26-722 [b]

Looks like CEC code requires a dedicated microwave circuit paralleling NEC code.
__________________
Normal people believe that if it ain't broke, don't fix it.
Engineers believe in fixing it so that it never breaks.
tdf-texas is offline   Reply With Quote
Old 06-02-2018, 01:39 AM   #62
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by tdf-texas View Post
Did some Google research on Canadian code and found this:
26-720 [d] Each receptacle installed in a cupboard, wall cabinet or enclosure for the use of a microwave oven in accordance with rule 26-710 [i] shall be supplied by a branch circuit that does not supply any other outlets and this circuit shall not be considered as forming part of the circuits required under rule 26-722 [b]

Looks like CEC code requires a dedicated microwave circuit paralleling NEC code.
That makes sense, and Canadian residential kitchens do have dedicated microwave circuits.

A question might be whether CSA Z240 RV requires everything in the codes which it references, or only those specific provisions which it lists.

Another question might be whether or not RVs in Canada are required to follow the Canadian Electrical Code, and similarly whether or not RVs in the U.S. are required to follow the National Electrical Code. They're not buildings; they're more like very big appliances which get plugged in sometimes, or very well equipped vehicles.
Brian B-P is offline   Reply With Quote
Old 06-02-2018, 04:55 AM   #63
Senior Member
 
Slickheadhunter's Avatar
 
Join Date: Oct 2014
Location: Weare, New Hampshire
Trailer: 2015 Escape 17A
Posts: 428
I have no idea about any of the electrical codes( completely electrically ignorant! ) but I know for a fact the microwave is routed through the outside GFI outlet, and not on its own breaker. I'm just super happy it's fixed.
Slickheadhunter is offline   Reply With Quote
Old 06-02-2018, 08:12 AM   #64
Senior Member
 
tdf-texas's Avatar
 
Join Date: Nov 2015
Location: Baytown, Texas
Trailer: 2017 21' Escape - upgraded version
Posts: 2,697
Quote:
Originally Posted by Brian B-P View Post
That makes sense, and Canadian residential kitchens do have dedicated microwave circuits.

A question might be whether CSA Z240 RV requires everything in the codes which it references, or only those specific provisions which it lists.

Another question might be whether or not RVs in Canada are required to follow the Canadian Electrical Code, and similarly whether or not RVs in the U.S. are required to follow the National Electrical Code. They're not buildings; they're more like very big appliances which get plugged in sometimes, or very well equipped vehicles.
I don't know about Canada but here are the rules for the US. The NEC is merely a guideline; each local jurisdiction has the authority to accept all, part, or none of the NEC code and is the only legally binding authority in regard to electrical code requirements. The adopted local code is all that matters from a compliance standpoint.

As a RV travels between local jurisdictions, local codes can vary from town to town. The only RV specific NEC code is in Article 551, Recreational Vehicles and Recreational Vehicle Parks. Even Article 551 has to be adopted by the local jurisdiction to be enforceable.

So common sense has to prevail when deciding if NEC code applies to how the wiring is done in a RV. NEC (and CEC) codes were derived from knowledge obtained from reviewing past failures which caused damage or death. It is a code which when followed will prevent making electrical mistakes that could cause you harm. Given that following electrical code will protect you, which codes should you ignore?
__________________
Normal people believe that if it ain't broke, don't fix it.
Engineers believe in fixing it so that it never breaks.
tdf-texas is offline   Reply With Quote
Old 06-02-2018, 08:41 AM   #65
Senior Member
 
tdf-texas's Avatar
 
Join Date: Nov 2015
Location: Baytown, Texas
Trailer: 2017 21' Escape - upgraded version
Posts: 2,697
I want to apologize to the OP of this thread for the side conversation on electrical codes. As you can probably tell by now, I am used to giving class lectures on electrical codes and how they apply.

To the OP.

I would try to get your wiring looked at by someone who understands wiring requirements. Having the microwave circuit with multiple outlets may haunt you with spurious trips on the occasions that too much load was applied to the breaker supplying the microwave. At the same time, they might want to look at the rest of the wiring - that wire should never have been wrapped around a screw. What else is there that might give you grief?
__________________
Normal people believe that if it ain't broke, don't fix it.
Engineers believe in fixing it so that it never breaks.
tdf-texas is offline   Reply With Quote
Old 06-02-2018, 09:02 AM   #66
Senior Member
 
Join Date: Mar 2013
Location: North of Danbury, Wisconsin
Trailer: 2018 Escape 21C
Posts: 3,033
I added a separate 20 amp circuit to the kitchen and split the microwave off from the kitchen circuit
I also taught code classes for journeyman electricians required to renew their state electrical license so I can empathize with TDF
I helped a buddy rewire part of his brand new $50 K sticky trailer .
His whole kitchen , living room , outside receptacle and part of the bedroom was on
ONE 15 amp circuit . Made it tough to make coffee and toast at the same time
steve dunham is offline   Reply With Quote
Old 06-02-2018, 09:27 AM   #67
Senior Member
 
rubicon327's Avatar
 
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,146
Quote:
Originally Posted by Slickheadhunter View Post
I have no idea about any of the electrical codes( completely electrically ignorant! ) but I know for a fact the microwave is routed through the outside GFI outlet, and not on its own breaker. I'm just super happy it's fixed.
Good job finding the issue. I was going to suggest checking the outside GFI but didn’t think it would be wired that way.
rubicon327 is offline   Reply With Quote
Old 06-02-2018, 09:39 AM   #68
Senior Member
 
Slickheadhunter's Avatar
 
Join Date: Oct 2014
Location: Weare, New Hampshire
Trailer: 2015 Escape 17A
Posts: 428
Here's a picture of the breakers and one of the metal outside outlet box from under the seat.
Attached Images
 
Slickheadhunter is offline   Reply With Quote
Old 06-02-2018, 09:42 AM   #69
Senior Member
 
Slickheadhunter's Avatar
 
Join Date: Oct 2014
Location: Weare, New Hampshire
Trailer: 2015 Escape 17A
Posts: 428
Here's the breakers.
Attached Images
 
Slickheadhunter is offline   Reply With Quote
Old 06-02-2018, 09:46 AM   #70
Senior Member
 
Slickheadhunter's Avatar
 
Join Date: Oct 2014
Location: Weare, New Hampshire
Trailer: 2015 Escape 17A
Posts: 428
For some reason these pictures are sideways.

The wire you see on the left goes from that outlet to a third outlet. The wire on the right with the electrical tape on it is the one going to the microwave. The screw in the center is where the wire was looped around and wore through.
Slickheadhunter is offline   Reply With Quote
Old 06-02-2018, 09:49 AM   #71
Senior Member
 
Slickheadhunter's Avatar
 
Join Date: Oct 2014
Location: Weare, New Hampshire
Trailer: 2015 Escape 17A
Posts: 428
The wire on the left going to the third outlet is covered with a black plastic corrugated covering, which I had to stuff around the wire going into the metal box because of the sharp metal around that hole.
Slickheadhunter is offline   Reply With Quote
Old 06-02-2018, 10:16 AM   #72
Senior Member
 
rubicon327's Avatar
 
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,146
Quote:
Originally Posted by Ron in BC View Post
Yes, and to further compound the situation, Circuit # 1 has two wires on the same breaker terminal. The first time that I acquainted myself with the panel the machine screw holding them was loose, still contact, but loose.

Ron
Ron: This seems odd. When I replaced the WFCO main board my converter hot was twinned on a 15A breaker with the fridge with a “utility pigtail”. I thought this was common practice so that only one wire is under the breaker lug and then it splits to serve two items.

The instructions from Progressive Dynamics specifically said: “If the utility pigtail was used on the original installation, two short lengths of 14AWG wire and a wire nut may be used to provide the utility pigtail. DO NOT install (2) wires into the breaker.”
rubicon327 is offline   Reply With Quote
Old 06-02-2018, 10:23 AM   #73
Site Team
 
rbryan4's Avatar
 
Join Date: Jun 2014
Location: Canyon Lake, Texas
Trailer: 2015 19 "Past Tents", 2021 F150 Lariat 2.7L EB
Posts: 10,222
Quote:
Originally Posted by rubicon327 View Post
Ron: This seems odd. When I replaced the WFCO main board my converter hot was twinned on a 15A breaker with the fridge with a “utility pigtail”. I thought this was common practice so that only one wire is under the breaker lug and then it splits to serve two items.

The instructions from Progressive Dynamics specifically said: “If the utility pigtail was used on the original installation, two short lengths of 14AWG wire and a wire nut may be used to provide the utility pigtail. DO NOT install (2) wires into the breaker.”
I haven't swapped out the mainboard yet, but mine has a utility pigtail coming off that breaker as well. Looks to me like two wires on that breaker wouldn't be secure.
__________________
"You can't buy happiness, but you can buy an RV. And that is pretty close."
rbryan4 is offline   Reply With Quote
Old 06-02-2018, 12:04 PM   #74
Senior Member
 
Slickheadhunter's Avatar
 
Join Date: Oct 2014
Location: Weare, New Hampshire
Trailer: 2015 Escape 17A
Posts: 428
Quote:
Originally Posted by rubicon327 View Post
Good job finding the issue. I was going to suggest checking the outside GFI but didn’t think it would be wired that way.
I didn't either, you would think a microwave would have its own GFI outlet and have its own breaker.
Slickheadhunter is offline   Reply With Quote
Old 06-02-2018, 12:35 PM   #75
Senior Member
 
tdf-texas's Avatar
 
Join Date: Nov 2015
Location: Baytown, Texas
Trailer: 2017 21' Escape - upgraded version
Posts: 2,697
This thread reminds me of a discussion the forum went through on the quality of Escape's wiring back before I picked up my trailer. The number of splices, wires changing color from point to point, dubious layout of breakers to outlets - it is all coming back to me. My comment at that time was that if my trailer had wiring like the examples depicted in that thread, I would rewire it soon after I picked up the trailer.

Well, with few exceptions, I have rewired my trailer since I picked it up! There is not a single wire that I have not inspected and then either rerouted, or replaced, or repaired. I found loose splices, loose neutral and ground terminations, doubled wires on breakers, multiple outlets on what should have been dedicated circuits - the list goes on.

I know that the wiring on Escape trailers is probably better than that on most of the RV's built but I had hoped for more. How do we help Escape get better at this?

Maybe the answer is feedback. If Escape doesn't know what the problems are - how can they make the trailers better. It doesn't cost any more to do the job right in the first place - they just need to know what "right" is. When we find issues that don't seem to be the way they should be, we should let Escape know. They may decide that the way they do it is the correct way for them but at least give them the chance to improve by letting them know.

The OP has a trailer that seems to have the microwave circuit wired kinda strange. Looping a wire over a screw, multiple outlets on the microwave circuit, wiring entering a metal box without bushings or clamps, a microwave on a outside outlet GFCI? - Escape should be informed that there are better wiring methods than these.

Comments?
__________________
Normal people believe that if it ain't broke, don't fix it.
Engineers believe in fixing it so that it never breaks.
tdf-texas is offline   Reply With Quote
Old 06-02-2018, 12:49 PM   #76
Senior Member
 
Slickheadhunter's Avatar
 
Join Date: Oct 2014
Location: Weare, New Hampshire
Trailer: 2015 Escape 17A
Posts: 428
Strictly from a safety standpoint I agree! The majority of people buying trailers from escape probably don't know very much about wiring( that would be me!)

I'm glad my trailer is small with minimal electrical devices!
Slickheadhunter is offline   Reply With Quote
Old 06-02-2018, 01:03 PM   #77
Senior Member
 
Join Date: Mar 2013
Location: North of Danbury, Wisconsin
Trailer: 2018 Escape 21C
Posts: 3,033
Quote:
Originally Posted by tdf-texas View Post
This thread reminds me of a discussion the forum went through on the quality of Escape's wiring back before I picked up my trailer. The number of splices, wires changing color from point to point, dubious layout of breakers to outlets - it is all coming back to me. My comment at that time was that if my trailer had wiring like the examples depicted in that thread, I would rewire it soon after I picked up the trailer.

Well, with few exceptions, I have rewired my trailer since I picked it up! There is not a single wire that I have not inspected and then either rerouted, or replaced, or repaired. I found loose splices, loose neutral and ground terminations, doubled wires on breakers, multiple outlets on what should have been dedicated circuits - the list goes on.

I know that the wiring on Escape trailers is probably better than that on most of the RV's built but I had hoped for more. How do we help Escape get better at this?

Maybe the answer is feedback. If Escape doesn't know what the problems are - how can they make the trailers better. It doesn't cost any more to do the job right in the first place - they just need to know what "right" is. When we find issues that don't seem to be the way they should be, we should let Escape know. They may decide that the way they do it is the correct way for them but at least give them the chance to improve by letting them know.

The OP has a trailer that seems to have the microwave circuit wired kinda strange. Looping a wire over a screw, multiple outlets on the microwave circuit, wiring entering a metal box without bushings or clamps, a microwave on a outside outlet GFCI? - Escape should be informed that there are better wiring methods than these.

Comments?
There is a huge difference between meeting the code and best trade practice
The pictures posted in this thread show a prime example of a poor wiring practices
The problem seem to be one of lack of knowledge and lack of training.
The NEC code book rules are the bare minimum and Art 100 states that the code is not a design manual nor that wiring installed to code is adequate for the purpose nor that it is a training manual.
TDF is correct in that it is not more expensive to do it right but first you have to know what RIGHT is.
I did a lot of things when I worked as an electrician not because it was code but because I knew from experience , what worked best , did not lead to failures at a later date and what would work best for the customer .
steve dunham is offline   Reply With Quote
Old 06-02-2018, 02:04 PM   #78
Senior Member
 
Join Date: Feb 2010
Location: Alcoa, Tennessee
Trailer: 2015 5.0 TA
Posts: 419
Don't know if anyone else mentioned this, but my TA has a separate breaker box attached to the underside of the driver side seat in the corner. I had no power to one side of the trailer and had just about given up when I happened to see a box with a breaker switch up there. That was the one that was tripped.
__________________
2015 Escape 5 TA
2016 Ford F-150
captmath is offline   Reply With Quote
Old 06-02-2018, 02:25 PM   #79
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by tdf-texas View Post
I would try to get your wiring looked at by someone who understands wiring requirements. Having the microwave circuit with multiple outlets may haunt you with spurious trips on the occasions that too much load was applied to the breaker supplying the microwave.
Sure, but this is not a unique situation in Escapes. How many of them have a dedicated microwave circuit? Based on previous discussions, I would guess not many.
Brian B-P is offline   Reply With Quote
Old 06-02-2018, 02:30 PM   #80
Senior Member
 
Join Date: Dec 2012
Location: Edmonton, Alberta
Trailer: 1979 Boler B1700
Posts: 14,935
Quote:
Originally Posted by rubicon327 View Post
When I replaced the WFCO main board my converter hot was twinned on a 15A breaker with the fridge with a “utility pigtail”. I thought this was common practice so that only one wire is under the breaker lug and then it splits to serve two items.”
That's what Escape did in Ron's case for "circuit #2", but not for the converter and microwave ("circuit #1").

Quote:
Originally Posted by rubicon327 View Post
The instructions from Progressive Dynamics specifically said: “If the utility pigtail was used on the original installation, two short lengths of 14AWG wire and a wire nut may be used to provide the utility pigtail. DO NOT install (2) wires into the breaker.”
That looks like good advice to follow, to me. The WFCO installation instructions don't say anything on this subject.
Brian B-P is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off




» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Escape Trailer Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -5. The time now is 08:46 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2023 Social Knowledge, LLC All Rights Reserved.