09-20-2021, 08:08 PM
|
#1
|
Member
Join Date: May 2019
Location: Lake County, California
Trailer: 2019 Escape 21 and a less than thrilled 2017 Tacoma dragging it around the countryside
Posts: 74
|
No GFCI trip on GFCI labeled circiut
While checking circuits for correct labeling in my 2019 E21' based on Centex's informative thread " Tip - Map what's Really on your breakers and fuses"
https://www.escapeforum.org/forums/f...tml#post396715
I discovered the following : the 120v. duplex outlet located in the cabinet face in front of the sink that is labeled "GFCI protected outlet" apparently isn't. There are no test and reset buttons on the duplex receptacle face, ergo the circuit trip must be a GFCI breaker yes? Well, it isn't.
The breaker for the circuit, one of the two 15a. trips located in the panel box separate from the WFCO power center has no test/reset function. And it's not as though they just put the Romex into the wrong breaker, neither of them are GFCI trip breakers.
So is there a third option for a GFCI trip location on this circuit? I can't imagine so but if I've missed the obvious, please, clue me in.
Granted, this is not a huge deal for me, I'm quite capable of swapping out one breaker for another, nor am I prone to mixing electricity and water on a regular basis, but it might be important to others in the Escape community so I'm posting it here as an FYI.
It seems like another unforced error on ETI's part. I'm not ETI bashing here, my trailer is light years ahead of anything built by Forest Floor Elkhart but a missing GFCI trip could be a fairly egregious error in the wrong hands.
Unless, as stated above, I've just missed the obvious.
For those who want to know, both breakers in the separate panel box are labeled the following:
TYPE BR115
TYPE C115
120/240V.~
Cu/Al SWD
HACR TYPE
1 POLE J969
E7819-T
__________________
Richard
Is it too many people or not enough beach?
|
|
|
09-20-2021, 08:17 PM
|
#2
|
Senior Member
Join Date: Apr 2019
Location: Wickenburg, Arizona
Trailer: 2019 E19
Posts: 133
|
Check your outside receptacle. That one should be a GFI receptacle. The receptacles inside your trailer (most of them) will probably be "downstream" of the GFI receptacle.
|
|
|
09-20-2021, 08:33 PM
|
#3
|
Member
Join Date: May 2019
Location: Lake County, California
Trailer: 2019 Escape 21 and a less than thrilled 2017 Tacoma dragging it around the countryside
Posts: 74
|
Quote:
Originally Posted by wackyburggeezer
Check your outside receptacle. That one should be a GFI receptacle. The receptacles inside your trailer (most of them) will probably be "downstream" of the GFI receptacle.
|
That was it! Didn't think to check the exterior plug.
Thank you.
__________________
Richard
Is it too many people or not enough beach?
|
|
|
09-20-2021, 08:53 PM
|
#4
|
Senior Member
Join Date: Oct 2008
Location: Calgary, Alberta
Trailer: 2017 Escape 5.0 TA
Posts: 15,572
|
Quote:
Originally Posted by wackyburggeezer
Check your outside receptacle. That one should be a GFI receptacle. The receptacles inside your trailer (most of them) will probably be "downstream" of the GFI receptacle.
|
Only the galley is GFI protected by the exterior plug. Those two are the only ones in need.
__________________
2017 Escape 5.0 TA
2015 Ford F150 Lariat 3.5L EcoBoost
2009 Escape 19 (previous)
“Most folks are about as happy as they make up their minds to be.” — Abraham Lincoln
|
|
|
09-20-2021, 10:38 PM
|
#5
|
Senior Member
Join Date: Feb 2020
Location: East of Austin, Texas
Trailer: 2021 Escape 5.0 / 2022 F150 SuperCab
Posts: 2,964
|
usually ...
Quote:
Originally Posted by Jim Bennett
Only the galley is GFI protected by the exterior plug. Those two are the only ones in need.
|
Yep, and in the case of my 5.0 where I requested "Delete" of the exterior outlet they installed an interior GFCI outlet on the PS dinette bench face, with the galley outlet wired downstream of that one for protection.
Then, just to keep things interesting, there's this thread about a much older Escape (2012 17B) where the owner found a tripped interior GFCI outlet disabled the exterior outlets and his fridge AC power outlet!.
Who said things never change?
|
|
|
09-21-2021, 06:20 AM
|
#6
|
Senior Member
Join Date: Mar 2021
Location: Mesa, Arizona
Trailer: 2021 21NE
Posts: 516
|
We received our trailer last week and that exact outlet, in the galley area, doesn't appear to work. Yes, we reset the GFCI, but it still doesn't appear to be a live outlet. Any ideas?
|
|
|
09-21-2021, 06:30 AM
|
#7
|
Senior Member
Join Date: Aug 2015
Location: Benton County, Iowa
Trailer: 2013 Escape 21 Classic Number 6, pulled by 2018 Toyota Highlander
Posts: 8,281
|
Is your outside outlet functional when reset? That would be the first thing I would check. Then if so, I would check for current at your inside receptacle. On the back side, not just probing the plug in. Shut off the power when you’re working around these things I’d you pull the outlet out of the box and expose the back. Then check and then shut power off when you’re putting them back in place. Might just be a loose or unhooked wire.
Iowa Dave
__________________
Ain’t no trouble jacking a double Burma Shave
Dave
|
|
|
09-21-2021, 06:42 AM
|
#8
|
Senior Member
Join Date: Mar 2021
Location: Mesa, Arizona
Trailer: 2021 21NE
Posts: 516
|
Quote:
Originally Posted by Iowa Dave
Is your outside outlet functional when reset? That would be the first thing I would check. Then if so, I would check for current at your inside receptacle. On the back side, not just probing the plug in. Shut off the power when you’re working around these things I’d you pull the outlet out of the box and expose the back. Then check and then shut power off when you’re putting them back in place. Might just be a loose or unhooked wire.
Iowa Dave
|
Yes, the outside outlet is functional before/after reset. We did not go further than checking the plug in inside. We will pull the outlet and check for loose wires. This is the only issue with the electrical system. Thank you for your quick reply!
|
|
|
09-21-2021, 07:55 AM
|
#9
|
Senior Member
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,146
|
Quote:
Originally Posted by kathytony1985
We received our trailer last week and that exact outlet, in the galley area, doesn't appear to work. Yes, we reset the GFCI, but it still doesn't appear to be a live outlet. Any ideas?
|
Unfortunately the self-contained outlets that Escape is now using are crap and don't have good contact area internally where the wire engages. My bet is an installation error and they never checked the outlet. Or they checked the outlet but after some vibration going down the road it doesn't work. I haven't done it but I wonder if it is possible to replace a self-contained outlet with a shallow box and traditional outlet?
|
|
|
09-21-2021, 08:01 AM
|
#10
|
Senior Member
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,146
|
Quote:
Originally Posted by Jim Bennett
Only the galley is GFI protected by the exterior plug. Those two are the only ones in need.
|
For those of us with absorption refrigerators the 120V outlet is in the vented cavity that could see some moisture. I have wondered if this should technically be a GFI outlet.
|
|
|
09-21-2021, 08:17 AM
|
#11
|
Senior Member
Join Date: Mar 2021
Location: Mesa, Arizona
Trailer: 2021 21NE
Posts: 516
|
Quote:
Originally Posted by Iowa Dave
Is your outside outlet functional when reset? That would be the first thing I would check. Then if so, I would check for current at your inside receptacle. On the back side, not just probing the plug in. Shut off the power when you’re working around these things I’d you pull the outlet out of the box and expose the back. Then check and then shut power off when you’re putting them back in place. Might just be a loose or unhooked wire.
Iowa Dave
|
Yes, the outside outlet is functional before/after reset. We did not go further than checking the plug in inside. We will pull the outlet and check for loose wires. This is the only issue with the electrical system. Thank you for your quick reply!
|
|
|
09-21-2021, 08:18 AM
|
#12
|
Senior Member
Join Date: Oct 2008
Location: Calgary, Alberta
Trailer: 2017 Escape 5.0 TA
Posts: 15,572
|
Quote:
Originally Posted by rubicon327
For those of us with absorption refrigerators the 120V outlet is in the vented cavity that could see some moisture. I have wondered if this should technically be a GFI outlet.
|
Their protection purpose is for devices used in a moist area. The refrigerator is dry. I guess someone could possibly use it for something used outside when wet, but that is not the intention nor very likely.
Easy to change if you felt it needed.
__________________
2017 Escape 5.0 TA
2015 Ford F150 Lariat 3.5L EcoBoost
2009 Escape 19 (previous)
“Most folks are about as happy as they make up their minds to be.” — Abraham Lincoln
|
|
|
09-21-2021, 08:19 AM
|
#13
|
Senior Member
Join Date: Mar 2021
Location: Mesa, Arizona
Trailer: 2021 21NE
Posts: 516
|
Quote:
Originally Posted by rubicon327
Unfortunately the self-contained outlets that Escape is now using are crap and don't have good contact area internally where the wire engages. My bet is an installation error and they never checked the outlet. Or they checked the outlet but after some vibration going down the road it doesn't work. I haven't done it but I wonder if it is possible to replace a self-contained outlet with a shallow box and traditional outlet?
|
Or obtain a new self contained outlet and install it? We will be checking the outlet today to see if we can identify the issue.
|
|
|
09-21-2021, 08:20 AM
|
#14
|
Senior Member
Join Date: Aug 2015
Location: Benton County, Iowa
Trailer: 2013 Escape 21 Classic Number 6, pulled by 2018 Toyota Highlander
Posts: 8,281
|
Back in the day when We had 28 rental rental pavilions in the park system. We renovated every one of them one, at a time with a new panel, serving counter, lighting and at least 8 20 amp circuits. Every beaker in the box was a ground fault breaker. It worked great for us. We used a self designed 3/8 plate steel lockable enclosure for both the serving counter outlets and the panel. Never had anyone get electricity without a rental but many tried. We had a lock over the counter cover. If vandals chopped the lock and opened the little door they found a recessed bolt securing the access. We used a regular hex head bolt and ground it so it only had 5 sides. Then we used a “water key” curb stop socket welded onto a regular 1/2 inch extension to turn the bolt.
I’m sure they ( the great unknown vandal and electricity thief) might have been heard to say “Rats, foiled again.” or something like that. All code, all union electricians, all inspected. all Square D panels made in my home town at the time.
Vandalism in city parks is a huge problem.
Iowa Dave
__________________
Ain’t no trouble jacking a double Burma Shave
Dave
|
|
|
09-21-2021, 08:25 AM
|
#15
|
Senior Member
Join Date: Nov 2015
Location: Baytown, Texas
Trailer: 2017 21' Escape - upgraded version
Posts: 2,697
|
Quote:
Originally Posted by rubicon327
For those of us with absorption refrigerators the 120V outlet is in the vented cavity that could see some moisture. I have wondered if this should technically be a GFI outlet.
|
Going through the latest NEC code, you can use a GFCI but it is not required. Siince the fridge outlet is not "readily accessible" and a dedicated circuit, NEC code does not require it to be a GFCI - same as the fridge outlet in your home.
But again, it doesn't hurt to be a GFCI. What the outlet should be is a outdoor weatherproof outlet as it is exposed to splashing water.
Of course, mine is now in a outdoor weatherproof box with a regular outlet receptacle. I had to change it after the original got wet and burned.
https://www.amazon.com/Hubbell-Bell-.../dp/B0044FQX0I
https://www.amazon.com/Hubbell-Raco-.../dp/B003A47SXU
__________________
Normal people believe that if it ain't broke, don't fix it.
Engineers believe in fixing it so that it never breaks.
|
|
|
09-21-2021, 09:42 AM
|
#16
|
Senior Member
Join Date: Jan 2021
Location: Hazelwood, Missouri
Trailer: 2021 5.0
Posts: 794
|
Quote:
Originally Posted by rubicon327
For those of us with absorption refrigerators the 120V outlet is in the vented cavity that could see some moisture. I have wondered if this should technically be a GFI outlet.
|
When it comes to a GFI in a RV I don’t know what is required or by whom, but I do know a little about residential requirements.
In certain municipalities a GFI is required on all outside outlets and any interior outlets that are within 6 feet of a water faucet or shower head.
City Inspectors have to come into the property and sign off on this each time a new tenet is to move in.
A refrigerator isn’t required to have a GFI, I have installed new single plug outlets so as to avoid having a refrigerator plugged into a GFI.
This is to prevent the GFI outlet from switching off and food going bad.
I also use these single plug outlets to plug garbage disposals into, these outlets are right under the kitchen sinks and can be a pain to crawl under when the GFI has flipped off.
Both of these locations pass the inspections and avoid unnecessary future problems from a GFI.
Many refrigerators in your home are not compatible with GFI outlets, seems motors and GFI outlets don’t care for each other.
I stopped keeping track of which fridge is or isint and just and just use single dedicated line outlets for fridges and garbage disposals.
|
|
|
09-21-2021, 11:41 AM
|
#17
|
Senior Member
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,146
|
Quote:
Originally Posted by kathytony1985
Or obtain a new self contained outlet and install it? We will be checking the outlet today to see if we can identify the issue.
|
Yes that would be the easiest. Starting with a new self-contained outlet is probably the best bet depending on what you find. Since you are under warranty Escape should send you a new one. Could always do something different later if you felt the need. Sorry my brain always goes to what I think would be the ideal long term solution.
|
|
|
09-21-2021, 11:52 AM
|
#18
|
Senior Member
Join Date: Mar 2021
Location: Mesa, Arizona
Trailer: 2021 21NE
Posts: 516
|
Quote:
Originally Posted by rubicon327
I haven't done it but I wonder if it is possible to replace a self-contained outlet with a shallow box and traditional outlet?
|
We were wondering the same thing?
|
|
|
09-21-2021, 11:54 AM
|
#19
|
Senior Member
Join Date: Mar 2021
Location: Mesa, Arizona
Trailer: 2021 21NE
Posts: 516
|
Quote:
Originally Posted by rubicon327
Sorry my brain always goes to what I think would be the ideal long term solution.
|
Nothing wrong with that thinking! The whole point of getting that extra outlet is so we can plug in our induction cooktop. So if it doesn't work what is the point of having it? Right? We're going to eliminate every scenario before we contact ETI to see about getting a new outlet, or just go buy one at Home Depot and not have to wait on them.
|
|
|
09-21-2021, 12:12 PM
|
#20
|
Senior Member
Join Date: Mar 2016
Location: Burlington Twp., New Jersey
Trailer: 2010 Escape 19
Posts: 7,146
|
Quote:
Originally Posted by kathytony1985
Nothing wrong with that thinking! The whole point of getting that extra outlet is so we can plug in our induction cooktop. So if it doesn't work what is the point of having it? Right? We're going to eliminate every scenario before we contact ETI to see about getting a new outlet, or just go buy one at Home Depot and not have to wait on them.
|
For a high draw device like an induction cooktop it might be best to consider a traditional outlet if you can. Better contact area on the connections. I have seen examples of poor connections and arching inside the self-contained outlets. You'll see what I mean if you do a google search. Just an FYI I don't think a place like Home Depot sells self-contained outlets anyway but I could be wrong.
|
|
|
|
|